Off the top of my head I'm not sure about the spacing criteria but from what
I recall this exception allows for the use of pipe other than steel - namely
cpvc to be run in this room.

Jim Johnston, P.E.
Fire Protection Engineer
Inland Fire Protection, Inc
1100 Ahtanum Road
Yakima, WA 98903
Phone 509-248-4471
Fax 509-248-1180
[email protected]


-----Original Message-----
From: Dewayne Martinez [mailto:[email protected]] 
Sent: Wednesday, November 25, 2009 11:46 AM
To: [email protected]
Subject: Ordinary Hazard room in Light Hazard area

One of my salesmen is telling me that there is a rule in 13 which states
that if you have a room of ordinary hazard occupancy, under 400SF, in a
otherwise light hazard occupancy that you can use light hazard spacing
for this area.  Anyone here of this?
Thanks,
Dewayne Martinez
Design Build Fire Protection
New Berlin, WI