6.3.6.2 Pipe or tube listed for light hazard occupancies shall
be permitted to be installed in ordinary hazard rooms of otherwise
light hazard occupancies where the room does not exceed
400 ft2 (37 m2).

11.1.5.2 Systems with Multiple Hazard Classifications.
(3)*For systems with multiple hazard classifications where the
higher classification only lies within single rooms less than
or equal to 400 ft2 (37.2 m2) in area with no such rooms
adjacent, the water supply requirements for the principal
occupancy shall be used for the remainder of the system.
(There is a similar section in chapter 12)

A.11.1.5.2(3) When a light hazard occupancy, such as a school,
contains separate ordinary hazard rooms no more than 400 ft2
(37.2 m2), the hose stream allowance and water supply duration
would be that required for a light hazard occupancy.
(There is a similar section in chapter12 appendix A)

I think these are what your salesman is thinking of, it is not related to
head spacing.

Thom McMahon, SET
Firetech, Inc.
2560 Copper Ridge Dr
P.O. Box 882136
Steamboat Springs, CO 80488
Tel:  970-879-7952
Fax: 970-879-7926



-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Dewayne
Martinez
Sent: Wednesday, November 25, 2009 12:46 PM
To: [email protected]
Subject: Ordinary Hazard room in Light Hazard area

One of my salesmen is telling me that there is a rule in 13 which states
that if you have a room of ordinary hazard occupancy, under 400SF, in a
otherwise light hazard occupancy that you can use light hazard spacing for
this area.  Anyone here of this?
Thanks,
Dewayne Martinez
Design Build Fire Protection
New Berlin, WI
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to