Yep, yep, yep........I have to agree with Matt, put them above and below if it 
is a standard wood product 


Kevin Law, PE
Bechtel National, Inc.
Waste Treatment Project
Fire Protection Engineering
Work  (509) 371-3280
Cell    (509) 531-5715


-----Original Message-----
From: [email protected] 
[mailto:[email protected]] On Behalf Of Matt Grise
Sent: Tuesday, December 15, 2009 10:56 AM
To: '[email protected]'
Subject: RE: Drop Wood Ceiling

I would put sprinklers above. Check out 13 (2002) 8.14.1.1

You might check the product listing though, I have run into a few wood ceiling 
systems that are fire retardant treated.

Matt Grisé PE*, LEED AP
Sales Engineer
Alliance Fire Protection
*Licensed in KS & MO 

913.888.0647 ph
913.888.0618 f
913.927.0222 cell
www. AFPsprink.com 


-----Original Message-----
From: [email protected] 
[mailto:[email protected]] On Behalf Of Jimmy Waite
Sent: Tuesday, December 15, 2009 12:53 PM
To: AFSA Sprinkler Forum
Subject: Drop Wood Ceiling

Gentlemen,

 

We have a situation where an engineer in requiring sprinkler protection above a 
drop wood ceiling.  The building is light hazard and noncombustible, and we 
have obviously provided protection below the ceiling.  I can't place a code 
reference in defense of either side.  It would seem that we have adequately 
protected the wood ceiling by protecting the floor space below it.  On the 
other hand, the back of the wood ceiling would mean there are combustibles in a 
concealed space.  What is everyone's opinion?

 

Thanks,

 

Jimmy Waite

Design Engineer


Piedmont Fire Protection Systems, LLC                            

3609 Bastion Lane            

Raleigh, NC  27604


o: 919.212.2356  

f:  919.212.2357  

 <mailto:[email protected]> [email protected]

web:  <http://www.piedmontfire.com/> www.piedmontfire.com


 

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field) 
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to