The only way I would be comfortable not protecting this space is if there was 
non-combustible insulation covering the entire combustible surface thereby 
effectively eliminating the "space" in concealed. This is tricky and must be 
done properly, but I have seen it more than once.

Greg McGahan
Operations Manager

Living Water Fire Protection
1160 McKenzie Road
P.O. Box 877
Cantonment, Florida 32533
(850) 937.1850 | Fax (850) 937.1852 | Cell (850) 554.3231
[email protected]

-----Original Message-----
From: [email protected] 
[mailto:[email protected]] On Behalf Of Richardson, R
Sent: Tuesday, December 15, 2009 4:01 PM
To: [email protected]
Subject: RE: Drop Wood Ceiling

I would suggest that in this case you do not check with the AHJ.  NFPA 13 
clearly requires sprinklers in the space, unless the wood is FR.  Personally, I 
get annoyed with a phone call whose goal is to simply confirm what NFPA clearly 
states.  There are plenty of off-beat situations not clearly addressed by NFPA 
where a phone inquiry is required, this is not one of them.

Rich Richardson
Seattle Fire Department

-----Original Message-----
From: [email protected] 
[mailto:[email protected]] On Behalf Of njarendt tds.net
Sent: Tuesday, December 15, 2009 13:44
To: [email protected]
Subject: Re: Drop Wood Ceiling

Check with the authority having jurisdiction.  They are the ones that
ultimately will determine what is needed.  Contact up front with the AHJ
usually saves a lot in the long run.  I do plan review for 2 fire districts
and time and energy can be saved by this up front discussion on issues like
this.

Norm
On Tue, Dec 15, 2009 at 12:53 PM, Jimmy Waite <[email protected]>wrote:

> Gentlemen,
>
>
>
> We have a situation where an engineer in requiring sprinkler protection
> above a drop wood ceiling.  The building is light hazard and
> noncombustible,
> and we have obviously provided protection below the ceiling.  I can't place
> a code reference in defense of either side.  It would seem that we have
> adequately protected the wood ceiling by protecting the floor space below
> it.  On the other hand, the back of the wood ceiling would mean there are
> combustibles in a concealed space.  What is everyone's opinion?
>
>
>
> Thanks,
>
>
>
> Jimmy Waite
>
> Design Engineer
>
>
> Piedmont Fire Protection Systems, LLC
>
> 3609 Bastion Lane
>
> Raleigh, NC  27604
>
>
> o: 919.212.2356
>
> f:  919.212.2357
>
>  <mailto:[email protected]> [email protected]
>
> web:  <http://www.piedmontfire.com/> www.piedmontfire.com
>
>
>
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> For Technical Assistance, send an email to: [email protected]
>
> To Unsubscribe, send an email 
> to:[email protected]<to%[email protected]>
> (Put the word unsubscribe in the subject field)
>
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to