dI have a situation asI have a situation with a hazard as follow, double row
rack storage, commodity Class III encapsulated, maximum storage height 40’,
aisles, 10’ wide. Roof with a slope of 3.5%, maximum height of 47’3” and
38’6” minimum, total area to be protected with sprinklers 232.000 sqft, area
with ceiling heights above 45’ 57.000 sqft (approximately 25% of total area)
We're being up to 2’4” above the maximum height established by  NFPA, FM and
UL for a  K25.2 ESFR sprinklers.

Do Do you have a different recommendation than use IRAS and ceiling ELO
sprinklers?, maybe increase the design area or increase the sprinkler
working pressure for the ESFR and remove or reduce the levels of IRAS.

Regards,

José Saldivia.
Incisan Fire C.A.
Venezuela.