Jose, I would suggest contacting Reliable sprinkler. I recall hearing something about a listing they got over 45'-0" ceiling with there HL22 ESFR. Max 48'-0" building and max storage height of 43ft with no in-rack spkrs. Not sure about encapsulated product.
Take a look at this link under HL22 midway down the page. http://www.reliablesprinkler.com/new_products.php Good luck Ken Holsopple -----Original Message----- From: [email protected] [mailto:[email protected]] On Behalf Of Jose Saldivia Sent: Wednesday, December 16, 2009 5:04 PM To: [email protected] Subject: ESFR K 25.2 SPRINKLER AT 47 FEET HEIGHT CEILING ALTERNATIVES. dI have a situation asI have a situation with a hazard as follow, double row rack storage, commodity Class III encapsulated, maximum storage height 40, aisles, 10 wide. Roof with a slope of 3.5%, maximum height of 473 and 386 minimum, total area to be protected with sprinklers 232.000 sqft, area with ceiling heights above 45 57.000 sqft (approximately 25% of total area) We're being up to 24 above the maximum height established by NFPA, FM and UL for a K25.2 ESFR sprinklers. Do Do you have a different recommendation than use IRAS and ceiling ELO sprinklers?, maybe increase the design area or increase the sprinkler working pressure for the ESFR and remove or reduce the levels of IRAS. Regards, José Saldivia. Incisan Fire C.A. Venezuela. _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [email protected] To Unsubscribe, send an email to:[email protected] (Put the word unsubscribe in the subject field) _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [email protected] To Unsubscribe, send an email to:[email protected] (Put the word unsubscribe in the subject field)