I think some time ago we asked for an interpretation from ICC and were
told that vents are required with ESFR's if the egress distance
exception is taken. If I can find a record of the emails I'll let you
know. It may also have been a topic on the ICC Forum.

Ron Fletcher
Aero Automatic
Phoenix, AZ


-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of George
Church
Sent: Thursday, December 17, 2009 7:04 AM
To: [email protected]
Subject: RE: ESFR DOES WHAT???

Vince, we did a job last year where our variance was approved and here's
the
logic train:

Egress distance can be increased past 250' if heat and smoke vents are
provided. 
So we "pencil vents in". 
Then we provide an ESFR system so the vents aren't required, erase them.
Extended egress distance in section labeled Extended egress distance
with
heat and smoke Vents was basis for the increase granted, but none of
them
were installed.

The architect chairing the variance committee voted for us, the other
two
guys split, it carried.

Yes, you can omit H&S vents with ESFR but I'd read the fine print and if
you
need to, as the top example illustrates, about anything is possible with
linguistics.

glc


-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Vince
Sabolik
Sent: Thursday, December 17, 2009 8:48 AM
To: [email protected]
Subject: ESFR DOES WHAT???

Good morning, forum --

I want to use control mode heads in an existing warehouse building 
under 30 ft in height.

Somebody (working for the owner) says that he would prefer ESFR heads 
because (his thought)
it eliminates the requirement for heat and smoke vents.

If that's true, I would have thought that the sprinkler 
manufacturer's marketing people would have
jumped all over this.

That aside, has anybody else ever run into anything like this?

                                                               thanks! 
Merry Christmas!

                                                              Vince

Vince Sabolik
Christi Fire Protection, Inc.
11351 Pearl Road
Strongsville, Ohio 44136

T 440 572-7730  F 440 572-7719  Email: 
<mailto:[email protected]>[email protected]

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email
to:[email protected]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email
to:[email protected]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to