FDC goes on pump discharge side.
Pump not smart enough to know FD took 50 PSI suction from city and boosted
it to 150, so now your pump discharge is 250 PSI.
Plug pit, install FDC on side of building.


-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Brian Harris
Sent: Wednesday, January 06, 2010 4:06 PM
To: [email protected]
Subject: RE: Fire Pumps & FDC's

I have a system with (2) Risers, (1) wet & (1) dry, both being supplied from
the pump discharge. The FDC is located out at the street on the system side
of the RPZ.


Brian Harris
FDFP INC.

-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Richard
Lindner
Sent: Wednesday, January 06, 2010 3:54 PM
To: [email protected]
Subject: Re: Fire Pumps & FDC's

Need more info.  Multiple alarm valves?  but if I am understanding
correctly, the FDC needs to be connected after the fire pump and before the
alarm valves etc.