Or if required to be in yard, plug pit tee as George said, and come off the
pump discharge and pipe back UG to location. Have had to do that many a
time.

Bobby Gillett
Sr. Project Manager
Key Fire Protection, Inc.
(731) 424-0130 office  (731) 424-9285 fax 
(731) 267-4853 cell
[email protected]
 
 
-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of George Church
Sent: Wednesday, January 06, 2010 3:20 PM
To: [email protected]
Subject: RE: Fire Pumps & FDC's

FDC goes on pump discharge side.
Pump not smart enough to know FD took 50 PSI suction from city and boosted
it to 150, so now your pump discharge is 250 PSI.
Plug pit, install FDC on side of building.


-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Brian Harris
Sent: Wednesday, January 06, 2010 4:06 PM
To: [email protected]
Subject: RE: Fire Pumps & FDC's

I have a system with (2) Risers, (1) wet & (1) dry, both being supplied from
the pump discharge. The FDC is located out at the street on the system side
of the RPZ.


Brian Harris
FDFP INC.

-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Richard
Lindner
Sent: Wednesday, January 06, 2010 3:54 PM
To: [email protected]
Subject: Re: Fire Pumps & FDC's

Need more info.  Multiple alarm valves?  but if I am understanding
correctly, the FDC needs to be connected after the fire pump and before the
alarm valves etc.
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum


_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

No virus found in this incoming message.
Checked by AVG - www.avg.com 
Version: 9.0.725 / Virus Database: 270.14.127/2603 - Release Date: 01/06/10
01:35:00

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to