I think you are missing an underlying philosophical point to seismic  
protection.  Different parts of the system do one of two things:  they  
either move with the surrounding structure or they move differentially  
from that structure.  Since you are allowed to use such holes as the  
hanger and you are attaching the sway braces to the same main that are  
anchored to the same structural family, I'm going with they are in the  
move together portion of the system. As such, why do you want  
clearance?  Granted we are NOT talking branch lines that wave to their  
own tune.

Roland

On Jan 22, 2010, at 12:33 PM, Todd Williams wrote:

> I ma working on a job where the engineer wants to run the mains
> through penetrations in steel beams. The question came up about
> clearance between the penetration and the pipe. Section 9.3.4 does
> not specifically address beams, but it is referenced in the handbook
> commentary under 9.3.4.1. Any thoughts on what minimum penetration
> size is required?
>
> Todd G. Williams, PE
> Fire Protection Design/Consulting
> Stonington, Connecticut
> www.fpdc.com
> 860.535.2080
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> For Technical Assistance, send an email to: [email protected]
>
> To Unsubscribe, send an email to:[email protected]
> (Put the word unsubscribe in the subject field)
>

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to