Where's the conflict?

Ceiling pockets?  Just put a head in them as an example.  Can't imagine
there are storage issues.  Sloped clg? Why can't you design a system under
'99 over 1500 sq.ft.  Really screw with them and do 0.09 over 1950 for the
'99 with a bigger safety than the 0.1 over 1950 for the '07. Listed heads in
trusses?  '99 says blah, blah, blah or follow the listing, right?

Chris Cahill, P.E.
Fire Protection Engineer
Sentry Fire Protection, Inc.
 
763-658-4483
763-658-4921 fax
 
Email: [email protected]
 
Mail: P.O. Box 69
        Waverly, MN 55390
 
Location: 4439 Hwy 12 SW
              Waverly, MN 55390
-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of George Church
Sent: Thursday, January 28, 2010 10:20 AM
To: [email protected]
Subject: Quandry-design to two editions of 13?

I'm close to going postal. It's been over a year since I posed a question to
PA's departments of Health and Labor & Industry, and we've still yet to
receive other than conflicting direction. I'm sure this occurs in other
jurisdictions throughout the US and maybe someone has solved this, it
certainly is not unique to PA.

 

Summary:

PA DOH enforces compliance with the 1999 edition of NFPA 13 because it is
the referenced edition in the 2000 Life Safety Code used by the Centers for
Medicare and Medicaid Services (Federal Health and Human Services). Both PA
DOH and CMS itself have reiterated clearly that they will accept ONLY
compliance with the 1999 edition; they really don't care if a newer code is
deemed equal or better protection by NFPA, or what edition of NFPA 13 is
referenced by the applicable local building code. 

 

PA's Dept of Labor and Industry is charged with administration and
enforcement of the PA Uniform Construction Code, now based on the 2009
I-Codes, so NFPA 13-2007 edition is now our standard. Under Pennsylvania
law, all facilities that are regulated by the Health Care Facilities Act
must also comply with the requirements of the Pennsylvania Construction Code
Act and its regulations.

 

Quandry:

So- how do we design a system to simultaneously comply with both 1999 and
(for now) 2007 editions of NFPA 13?

 

We cannot comply simply with the more recent standard as equal or better,
that'd be too easy. CMS and DOH have both stated this is unacceptable.

 

Now we're certainly not the only sprinkler contractor doing work in health
care and nursing homes where CMS mandates apply- i.e., anywhere
reimbursement for services is covered by Medicare and/or Medicaid. And PA is
not the only state adopting a code with post-1999 #13 as the adopted
standard.

 

What are the rest of you doing to comply? 

 

George Church

Rowe Sprinkler

 

 

 

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to