George,

If you haven't already, try Hellan strainers 
http://www.hellanstrainer.com/.

I've used them before, not with sand straining, but the unique design may 
be just what you're looking for. They claim they can filter out sand. 
Hellan is the Cadillac so the strainer could be pricey.

Regards,

James L.(Jim) Roberts, PE/SET
Fluor Corporation
100 Fluor Daniel Drive
Greenville, SC 29607
864.281.5149






"George Church" <[email protected]>
Sent by:  [email protected]
02/04/2010 05:38 PM
Please respond to sprinklerforum

To
<[email protected]>
cc

Subject
RE: sand strainer?







Ok, let me re-phrase- 

Anyone know how to filter sand out of a supply?

-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Matt Grise
Sent: Thursday, February 04, 2010 5:29 PM
To: '[email protected]'
Subject: RE: sand strainer?

Maybe a diesel generator powering an electric pump? Or perhaps a small
high-quality cooling water source?

Matt Grisé PE*, LEED AP 
Sales Engineer 
Alliance Fire Protection 
*Licensed in KS & MO 

913.888.0647 ph 
913.888.0618 f 
913.927.0222 cell 
www. AFPsprink.com 


-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of George 
Church
Sent: Thursday, February 04, 2010 4:32 PM
To: [email protected]
Subject: sand strainer?

We've got a problem child project where sand in the water supply clogs up
the cooling jacket on the diesel, and sand blasts the rubbers in valves so
they drip.

Small private water purveyor (the developer of the industrial park is the
owner) supplies our diesel which then feeds the systems, all interior 
piping
downstream of pump. Project located several miles from the ocean, a couple
miles from the Bay.

I can't imagine a strainer with perfs small enough to grab grains of sand
and not have atrocious friction loss. I can't find cheesecloth to wrap
around the strainer basket that's UL-Listed in a pump suction application.

While I haven't encountered this before, it likely isn't the first time 
the
problem has been encountered. Any one know a remedy other than a tank 
(with
settling basin?) and higher pressure 2,500 GPM pump to make up for the 
loss
of city residual pressure?

George Church
Rowe Sprinkler


_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

------------------------------------------------------------
The information transmitted is intended only for the person 
or entity to which it is addressed and may contain 
proprietary, business-confidential and/or privileged material.  
If you are not the intended recipient of this message you are 
hereby notified that any use, review, retransmission, dissemination, 
distribution, reproduction or any action taken in reliance upon 
this message is prohibited. If you received this in error, please 
contact the sender and delete the material from any computer.  

Any views expressed in this message are those of the individual 
sender and may not necessarily reflect the views of the company.  
------------------------------------------------------------
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to