Keep in mind you won't be able to take the QR design reduction based upon 
ceiling height unless all the sprinklers in your area are QR.

Ralphy

--- On Mon, 2/8/10, George Church <[email protected]> wrote:

From: George Church <[email protected]>
Subject: RE: mixing standard and QR spklrs in calc?
To: [email protected]
Date: Monday, February 8, 2010, 4:18 PM

So they're changing out the classrooms to QR, but leaving the Light hazard
Corridors that constitute the egress path as SR. Go figure.

-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Matthew J.
Willis
Sent: Monday, February 08, 2010 11:04 AM
To: [email protected]
Subject: RE: mixing standard and QR spklrs in calc?

Since you are using large room it should not. If you were using area, you
could not take the reduction.

R/
Matt

 
Matthew J. Willis, CET
Automatic Fire Sprinklers
Norred Fire Systems L.L.C.
318-387-1134 Voice
318-387-1163 Facsimile
[email protected]
-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Todd Williams
Sent: Monday, February 08, 2010 10:01 AM
To: [email protected]
Subject: mixing standard and QR spklrs in calc?

I am working on a system for a school where the systems in some 
existing classrooms are going to be modified and all QR sprinklers 
are going to be installed. The hydraulic area I plan to use is one 
classroom of 4-6 sprinklers and two sprinklers in the corridor (meets 
requirements). The corridor sprinkler are standard response. That 
wouldn't effect the hydraulics in this situation would it?

Todd G. Williams, PE
Fire Protection Design/Consulting
Stonington, Connecticut
www.fpdc.com
860.535.2080  
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)



      
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to