Chad, I think that you may be overthinking it. If the vertical obstruction is more than 18" below the deflector, you have enough room for the spray pattern umbrella to form to its full diameter. Shadowing that would occur in your example is fine, because remember, the purpose of sprinklers is to control and contain! If the sprinkler keeps the fire confined to the shadowed area by wetting combustibles around it, then its done its job.
Well wait, I just read through this section in the '07 handbook, thinking that I read something to the above effect in the explanitory text, however I can't find it now. Maybe I'm under thinking it. On Wed, Feb 10, 2010 at 3:00 PM, Chad <[email protected]> wrote: > Bob, > > That is what I getting at. If you can ignore the partition for spacing the > sprinklers, you are going to have individual cubicals that are going to get > a shadowing effect that will not allow the floor space to get adequate > coverage. Also, theoretically, you could have a cubical that will have > floor coverage greater than 130 sq. ft. using the s x l rules. If you had > to take the partitions into account, you could not have the sprinkler > exceed > 130 sq. ft. using the s x l. > > My concern is that a fire marshal will come back with this argument and > NFPA > will not have a definitive response or am I thinking to much? > Thanks, > > Gregg Fontes > Cen-Cal Fire Systems, Inc. > 11780 North Hwy. 99 > Lodi, CA 95240 > Phone (209) 334-9119 > Fax (209) 334-2923 > > > -----Original Message----- > From: [email protected] > [mailto:[email protected]] On Behalf Of Bob Knight > Sent: Wednesday, February 10, 2010 11:08 AM > To: [email protected] > Subject: RE: Floor Mount Vertical Obstructions > > Greg said, "So regardless of light or ordinary hazard". > The obstruction criteria for Vertical Obstructions can only be applied to > Light Hazard. Therefore, I don't believe that you can apply it to the > storage compartments. Maybe what you are saying is that if you position a > sprinkler directly over top of a partition wall than it could be 7' either > direction to the next wall and not be affected? Otherwise, the shadowing > created by the vertical obstruction would be huge and the ability of the > sprinkler to adequately control the fire would be greatly reduced due to > the > potential fuel load in any given storage compartment. > > Anyway, just my two cents for the day, > > Bob Knight > > -----Original Message----- > From: [email protected] > [mailto:[email protected]] On Behalf Of Chad > Sent: Wednesday, February 10, 2010 11:45 AM > To: [email protected] > Subject: RE: Floor Mount Vertical Obstructions > > So the chart for Light Hazard occupancy shows that if the vertical distance > is 18", than the sprinkler has to be 30" or more from the vertical > obstruction. So regardless of light or ordinary hazard, you can ignore the > vertical obstructions if they are greater than 18" down? So If you can > ignore the vertical partitions due to them being greater than 18" below, > you > can also ignore any horizontal spacing to the partitions. You could end up > with a sprinkler horizontally 7' off of two walls of the individual > cubical. > Therefore, the s x l would not apply to each individual cubical, since > theoretically, there are no partitions. Correct? > > > > Thanks, > > Gregg Fontes > > Cen-Cal Fire Systems, Inc. > 11780 North Hwy. 99 > Lodi, CA 95240 > Phone (209) 334-9119 > Fax (209) 334-2923 > > No virus found in this outgoing message. > Checked by AVG - www.avg.com > Version: 9.0.733 / Virus Database: 271.1.1/2679 - Release Date: 02/10/10 > 00:40:00 > > _______________________________________________ > Sprinklerforum mailing list > [email protected] > http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum > > For Technical Assistance, send an email to: [email protected] > > To Unsubscribe, send an email > to:[email protected]<to%[email protected]> > (Put the word unsubscribe in the subject field) > > _______________________________________________ > Sprinklerforum mailing list > [email protected] > http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum > > For Technical Assistance, send an email to: [email protected] > > To Unsubscribe, send an email > to:[email protected]<to%[email protected]> > (Put the word unsubscribe in the subject field) > -- Benjamin Young Sprinkler Designer Rowe Sprinkler Systems, Inc. [email protected] _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [email protected] To Unsubscribe, send an email to:[email protected] (Put the word unsubscribe in the subject field)