Chris,

Now that makes sense.  I didn't think about the vertical drop of the spray
pattern.  If the full spray pattern is developed in the first 18", there
should not be much of a shadow effect.  Good point.  

Thanks,
Gregg Fontes 
Cen-Cal Fire Systems, Inc.
11780 North Hwy. 99
Lodi,  CA   95240
Phone (209)  334-9119
Fax (209)  334-2923

 

-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Chris Cahill
Sent: Wednesday, February 10, 2010 12:25 PM
To: [email protected]
Subject: RE: Floor Mount Vertical Obstructions

Two more thoughts.  

First, where does NFPA 13 say head 5'6" above walls or other obstructions
are an issue in any occupancy including HPS of flammable liquids?  We don't
put head in each aisle in HPS with over 3' from storage to head.  Lesser
hazards it's 18", IMHO.  If LH you even have options less than 18"

Second, after a bit the droplets have changed from nearly horizontal
movement to nearly vertical.  By the time you are 5'6" down I'm sure all
movement is nearly vertical.  You can't have shadows from walls without
horizontal movement.  I believe most of this transition from horizontal to
vertical takes place in the first 18" but don't quote me on that. 

Chris Cahill, P.E.
Fire Protection Engineer
Sentry Fire Protection, Inc.
 
763-658-4483
763-658-4921 fax
 
Email: [email protected]
 
Mail: P.O. Box 69
        Waverly, MN 55390
 
Location: 4439 Hwy 12 SW
              Waverly, MN 55390

-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Chad
Sent: Wednesday, February 10, 2010 2:00 PM
To: [email protected]; [email protected]
Subject: RE: Floor Mount Vertical Obstructions

Bob,

That is what I getting at.  If you can ignore the partition for spacing the
sprinklers, you are going to have individual cubicals that are going to get
a shadowing effect that will not allow the floor space to get adequate
coverage.  Also, theoretically, you could have a cubical that will have
floor coverage greater than 130 sq. ft. using the s x l rules.  If you had
to take the partitions into account, you could not have the sprinkler exceed
130 sq. ft. using the s x l.   

My concern is that a fire marshal will come back with this argument and NFPA
will not have a definitive response or am I thinking to much?
Thanks, 
 
Gregg Fontes 
Cen-Cal Fire Systems, Inc.
11780 North Hwy. 99
Lodi,  CA   95240
Phone (209)  334-9119
Fax (209)  334-2923
 

-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Bob Knight
Sent: Wednesday, February 10, 2010 11:08 AM
To: [email protected]
Subject: RE: Floor Mount Vertical Obstructions

Greg said, "So regardless of light or ordinary hazard".
The obstruction criteria for Vertical Obstructions can only be applied to
Light Hazard.  Therefore, I don't believe that you can apply it to the
storage compartments.  Maybe what you are saying is that if you position a
sprinkler directly over top of a partition wall than it could be 7' either
direction to the next wall and not be affected?  Otherwise, the shadowing
created by the vertical obstruction would be huge and the ability of the
sprinkler to adequately control the fire would be greatly reduced due to the
potential fuel load in any given storage compartment.

Anyway, just my two cents for the day,

Bob Knight

-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Chad
Sent: Wednesday, February 10, 2010 11:45 AM
To: [email protected]
Subject: RE: Floor Mount Vertical Obstructions

So the chart for Light Hazard occupancy shows that if the vertical distance
is 18", than the sprinkler has to be 30" or more from the vertical
obstruction.  So regardless of light or ordinary hazard, you can ignore the
vertical obstructions if they are greater than 18" down?  So If you can
ignore the vertical partitions due to them being greater than 18" below, you
can also ignore any horizontal spacing to the partitions.  You could end up
with a sprinkler horizontally 7' off of two walls of the individual cubical.
Therefore, the s x l would not apply to each individual cubical, since
theoretically, there are no partitions.  Correct?   



Thanks,
 
Gregg Fontes
 
Cen-Cal Fire Systems, Inc.
11780 North Hwy. 99
Lodi,  CA   95240
Phone (209)  334-9119
Fax (209)  334-2923

No virus found in this outgoing message.
Checked by AVG - www.avg.com 
Version: 9.0.733 / Virus Database: 271.1.1/2679 - Release Date: 02/10/10
00:40:00

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to