I'm not talking about calculations just about selecting the actual size of
the pipe. Should I use a 1" pipe on 2 sprinklers or use a 1" pipe as long as
the gpms are less than 10. I just want to know how people know or choose the
size of pipe they use for each branch, sprig and main.

Karen Purvis
Senior Designer
Facility Systems Consultants
713 South Central Street,
Suite 101
Knoxville, TN 37902
ph.865-246-0164
fax 865-246-1084

-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Matt Grise
Sent: Wednesday, February 10, 2010 4:23 PM
To: '[email protected]'
Subject: RE: pipe sizing question

In some of the jurisdictions around here the AHJ's do allow submittals
without calcs for small add/relocate, and tenant improvement work as long as
it does not exceed the original hydraulic design of the shell system
(adjusting an OH2 retail system to accommodate a LH office, etc).

I am familiar with the pipe drop charts you are talking about. The main
issue I see with those is that it could be difficult to account for
over-flow at each head, so you could end up with more water flowing than you
anticipate.

Matt Grisé PE*, LEED AP 
Sales Engineer 
Alliance Fire Protection 
*Licensed in KS & MO 

913.888.0647 ph 
913.888.0618 f 
913.927.0222 cell 
www. AFPsprink.com 


-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Travis Mack,
SET
Sent: Wednesday, February 10, 2010 3:18 PM
To: [email protected]
Subject: Re: pipe sizing question

It is my understanding that you need to provide calculations per NFPA 
13, or use the pipe schedule method where it is allowed.  You can 
estimate with tables showing pressure drops, but that likely won't 
suffice for submittal to the local authorities in any where that I have 
done work.

On 2/10/2010 2:08 PM, Karen Purvis wrote:
> We mainly do new and add-on systems a few retrofits no grids no high piled
> storage no extra hazard. Usually all light and ordinary hazard.
>
> Karen Purvis
> Senior Designer
> Facility Systems Consultants
> 713 South Central Street,
> Suite 101
> Knoxville, TN 37902
> ph.865-246-0164
> fax 865-246-1084
> -----Original Message-----
> From: [email protected]
> [mailto:[email protected]] On Behalf Of
> [email protected]
> Sent: Wednesday, February 10, 2010 4:12 PM
> To: [email protected]
> Subject: RE: pipe sizing question
>
> For what kind of systems, new, retrofits, tree, grid, etc.....?
>
>
> Craig L. Prahl, CET
> Fire Protection Specialist
> Mechanical Department
> CH2MHILL
> Lockwood Greene
> 1500 International Drive
> PO Box 491, Spartanburg, SC  29304-0491
> Direct - 864.599.4102
> Fax - 864.599.8439
> [email protected]
> http://www.ch2m.com
>
>
> -----Original Message-----
> From: [email protected]
> [mailto:[email protected]] On Behalf Of Karen
Purvis
> Sent: Wednesday, February 10, 2010 3:57 PM
> To: [email protected]
> Subject: pipe sizing question
>
> This may seem like a very newbie question but here goes. How do most of
you
> guys size your pipe other than using a hydraulic calculation program? I
have
> been using a pressure drop chart that list pressure drop and velocity in
> schedule 40 pipe for water at 60°F per 100 feet drop. So far this has
worked
> for me but now I have someone questioning my method. Should I be going
back
> to the pipe schedule method?
>
>
>
> Karen Purvis
>
> Senior Designer
>
> Facility Systems Consultants
>
> 713 South Central Street,
>
> Suite 101
>
> Knoxville, TN 37902
>
> ph.865-246-0164
>
> fax 865-246-1084
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> For Technical Assistance, send an email to: [email protected]
>
> To Unsubscribe, send an email to:[email protected]
> (Put the word unsubscribe in the subject field)
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> For Technical Assistance, send an email to: [email protected]
>
> To Unsubscribe, send an email to:[email protected]
> (Put the word unsubscribe in the subject field)
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> For Technical Assistance, send an email to: [email protected]
>
> To Unsubscribe, send an email to:[email protected]
> (Put the word unsubscribe in the subject field)
>    


-- 
Please feel free to call if you have any questions or comments.

Sincerely,

Travis Mack, SET
MFP Design, LLC
2508 E Lodgepole Drive
Gilbert, AZ 85298
Office (480) 505-9271
Fax (866) 430-6107

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to