Tom,

As far as spacing, obstruction, etc are concerned, the key to answering your
question (IMHO) lies in understanding the difference between an INSPECTION
and a DESIGN EVALUATION. Both are referenced in Ch 4 of NFPA-25 (2008
edition).  

Regarding establishment of baseline dates for less-frequent-than-annual
activities, I'd just ask when applicable tasks were last done.  If there's
no evidence of completion within time frames as laid out in the standard,
they're due now. 

Drop me a note off-line if you'd like.

Best,  

PJ

Paul Johnson
Bardane, Inc. Build Value! 
(407) 401-7154 - Office
(407) 399-5081 - Mobile 
[email protected]
www.bardane.net 
 
 

-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Tom Duross
Sent: Friday, February 12, 2010 6:41 PM
To: [email protected]
Subject: NFPA 25 Inspections

How are you guys breaking out your inspections versus testing for systems?
So far for me, all I've been upgrading my old testing accounts to is to
suggest they have us do a cursory inspection for spacing, obstructions,
damage, etc., just visual.  I have a few clients whose insurers have
requested full compliance with NFPA 25 but with little explanation.  I tell
them it's a little like asking how long a piece of string is and that's the
wrong answer.  What I'm trying to break out is the tasks that become
requirements after the first year, per 25, but it gets complicated.

Brief example:

How are you approaching a client with a wet system installed in 1964 that
got a few years of tests by various sprinkler and alarm companies?  Are you
tracing back through your state codes for the applicable edition of 13A or
current referenced edition of 25?  How and why?

 

Thanks.

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to