They wouldn't even have to be in a bucket to be creeping, although I see the
clue to other improper handling procedures in general before/during
installation. But even with best intentions, are the Fed Ex trucks bringing
us the heads air conditioned? L O N G supply chain...

glc

-----Original Message-----
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of
craig.pr...@ch2m.com
Sent: Wednesday, February 17, 2010 4:04 PM
To: sprinklerforum@firesprinkler.org
Subject: RE: Accidental Fusing/unintended operation

We think of the installation conditions contributing to things like solder
creep due to heat exposure but what about the fitter with a bucket of heads
in the back of his truck on a hot August day parked in the shop where it's
over 100F?    Some failures could be the result of poor handling before
installation. 


Craig L. Prahl, CET   
Fire Protection Specialist
Mechanical Department
CH2MHILL
Lockwood Greene
1500 International Drive
PO Box 491, Spartanburg, SC  29304-0491
Direct - 864.599.4102
Fax - 864.599.8439
craig.pr...@ch2m.com
http://www.ch2m.com 


-----Original Message-----
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of
jhoff...@kcp.com
Sent: Wednesday, February 17, 2010 3:35 PM
To: sprinklerforum@firesprinkler.org; bcasterl...@fsc-inc.com
Subject: Re: Accidental Fusing/unintended operation

I think we are over-analyzing the incident.  Heads do fail occasionally.
Not frequently but sometimes.  This has happened here twice.  One was a
Grinnell Duraspeed back in 1997.  There was no heat source nearby that was
an obvious culprit.  It was installed in the factory area (25 feet
ceilings) along with hundreds of others.  The plant is air conditioned so
the ambient is less than 100 degrees F.  It was a 1968 brass head, 165
degree F issue C Duraspeed.

We sent it to our lab (yes, we have our own lab).  the scanning electron
microscope analysis showed elongation of the grains of metal in the solder
bond indicating creep.   However, they also saw some porosity in the
solder, which may have resulted in a less-than-standard ability to resist
the forces exerted on the link.  So the manufacturing process may not always
be perfect.

We then sent the parts to Grinnell for their analysis.  They determined that
the link separated due to creeping apart of the solder bond.  Their
microscopic viewing of the solder bond indicated that the surface texture
was similar in appearance to those that were known to be over-heated.
Over-heat is defined as an ambient over 100 degrees F.   There could have
been steam pipes in the area of the failed sprinkler at one time which may
have exposed this head to over-heat, but there were no steam pipes in the
area at the time of the failure.  We sent them several other heads that were
adjacent to the failed one and they did strength tests on the link and they
all tested normal.

For a 212 degree F sprinkler an overheat condition would be over 150
degrees, which an attic area in Kansas may or may not reach at one time or
another.  Our experience was that the sprinkler failed in the middle of the
day, years after any heat exposure, if there ever was heat exposure, for no
apparent reason.  Things fail sometimes.  Do lab analysis, send parts off to
the manufacturer but eventually you have to replace the head and move on.

John Hoffman P.E. | Fire Protection Engineer | Facility Engineering
Services, KCP, LLC - Burns & McDonnell Engineering | National Nuclear
Security Administration's Kansas City Plant | Operated by Honeywell FM&T |
2000 E. 95th St | Kansas City, MO  64131 | ph 816-997-7213

sprinklerforum-boun...@firesprinkler.org wrote on 02/17/2010 02:03:49 PM:

> [image removed]
>
> Accidental Fusing
>
> Brad
>
> to:
>
> sprinklerforum
>
> 02/17/2010 02:04 PM
>
> Sent by:
>
> sprinklerforum-boun...@firesprinkler.org
>
> Please respond to sprinklerforum, bcasterline
>
> -The change in pressure is half the density times the velocity 
> squared.-
>
>
>
> I have been asking myself these questions---
>
> 1-why had the head been through 6 summers without fusing- without a 
> manufacturing or installation defect showing up?
>
> 2-why had the head fused at 6:30 AM, not 9 hours earlier?
>
> If  it was due to "heat", the only answer could be a dynamic scenario
where
> the different conditions became "right"-
>
> an increase in THIS here, a decrease in THAT there. differences--- as 
> far
as
> "heat" goes, there is one between
>
> TEMPERATURE and QUANTITY. Quantity varies as the mass, Temperature as 
> the kinetic energy. I knew the only way
>
> for the Quantity to change is if the head gained or lost mass (the 
> higher velocity of the air at the head, the lower the pressure,
>
> the faster the solder vaporizes. maybe the old guy in the art room at 
> MU
did
> see that sprinkler vaporize).  Kinetic energy is
>
> half the mass times the velocity squared. For Temperature 
> measurements,
the
> AVERAGE velocity is theorized. When I think of
>
> an increase in the quantity of the air passing the head, I think of an 
> increase in the probability of  "fresh quantities of heat"-
>
> quantities with higher than average kinetic energies, which Would 
> raise
the
> temperature- (a bad example would be draining
>
> and charging wet systems frequently- introducing "fresh air").
>
> I have always been amazed at sprinklers-the fine line between going 
> off
when
> they are supposed to, but not until.
>
>
>
>
>
>
>
>
>
>
>
> _______________________________________________
> Sprinklerforum mailing list
> Sprinklerforum@firesprinkler.org
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> For Technical Assistance, send an email to: supp...@firesprinkler.org
>
> To Unsubscribe, send an email 
> to:sprinklerforum-requ...@firesprinkler.org
> (Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: supp...@firesprinkler.org

To Unsubscribe, send an email to:sprinklerforum-requ...@firesprinkler.org
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: supp...@firesprinkler.org

To Unsubscribe, send an email to:sprinklerforum-requ...@firesprinkler.org
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: supp...@firesprinkler.org

To Unsubscribe, send an email to:sprinklerforum-requ...@firesprinkler.org
(Put the word unsubscribe in the subject field)

Reply via email to