If the slope is only 3:12?

Sent from my iPhone

On Feb 22, 2010, at 12:53 PM, "Art Tiroly" <[email protected]>  
wrote:

> Check the TYCO attic sprinkler info again. With sloped roof in a  
> wood truss
> attic you can cover the 40-60ft wide attic with BB sprinklers at the  
> peak
> only spaced 6ft apart. They are available in K= 5.6 and 8.0 with  
> just one
> row at the peak. Attic Sprinklers are expensive but very efficient  
> install.
> Both wet and dry applications.
>
> Arthur Tiroly
> ATCO Fire Protection Design
> Tiroly and Associates
> 216-621-8899
> 216-570-7030 Cell
> WWW.ATCOfirepro.com
>
>
> -----Original Message-----
> From: [email protected]
> [mailto:[email protected]] On Behalf Of  
> Travis Mack,
> SET
> Sent: Sunday, February 21, 2010 4:41 PM
> To: [email protected]
> Subject: Attics and Tyco AP sprinklers
>
> Is it permissible to protect an attic entirely with Tyco AP  
> sprinklers?
> I am looking at a project with a 3:12 roof slope.  The Roof is */- 40'
> span.  Tyco makes a BB sprinkler that allows a 3:12 roof slope, but  
> a max
> span of 20'.  I do not see any criteria in the data sheet for the  
> Tyco Attic
> Sprinklers for a roof entirely protected with AP sprinklers, only a  
> mix of
> HIP, BB, SD & AP.
>
> Or, it is possible to put a row of the 4.2K BB sprinklers at the  
> ridge and
> then put a row of AP sprinklers at the eave to get the 40' roof span
> coverage.  In that way, the 4.2k BB would only be protecting up to 20'
> and the AP would get the last 10' on each side to give me my total  
> roof span
> of 40'.  The reason for doing this is to try to utilize CPVC piping  
> in the
> attic as well as the floors below where the CPVC is allowed without a
> problem.
>
> --
> Please feel free to call if you have any questions or comments.
>
> Sincerely,
>
> Travis Mack, SET
> MFP Design, LLC
> 2508 E Lodgepole Drive
> Gilbert, AZ 85298
> Office (480) 505-9271
> Fax (866) 430-6107
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> For Technical Assistance, send an email to: [email protected]
>
> To Unsubscribe, send an email to:Sprinklerforum- 
> [email protected]
> (Put the word unsubscribe in the subject field)
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> For Technical Assistance, send an email to: [email protected]
>
> To Unsubscribe, send an email to:Sprinklerforum- 
> [email protected]
> (Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to