Not sure if it was a mistype, but the figure in 8.6.3.2.3 shows 11.25 
ft...11'-3".  Your distance of 11'-4" seems to put you out of that ruling.

If it is less, and the distances from the existing sprinkler to both the 
rectangular walls and the assumed extension of the cove walls into the room are 
all less than 7'-6", I would say you meet the 225 sq. ft. maximum.  I say this 
because the code says "angled or irregular" which is how I would describe your 
situation.


-----Original Message-----
From: [email protected] 
[mailto:[email protected]] On Behalf Of Todd Williams
Sent: Tuesday, February 23, 2010 4:37 AM
To: [email protected]
Subject: angular alcove

An office is rectangular except for a small, V-shaped alcove. Minus
the alcove, the room could be protected by 2 sprinklers. If I apply
8.6.3.2.3 (13-2002), the distance between the existing sprinkler and
the corner is 11'-4", just within the 11'-5" maximum for that ruling.
I have used this section for rooms with tight angular walls, but
never for an angular alcove. Would this be an acceptable application?

Todd G. Williams, PE
Fire Protection Design/Consulting
Stonington, Connecticut
www.fpdc.com
860.535.2080
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

--
ExchangeDefender Message Security: Click below to verify authenticity
http://www.exchangedefender.com/verify.asp?id=o1NF9U36005623&[email protected]

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to