Forest,

When using those test cocks I presume you've been properly trained and
certified for touching a backflow device, only use the #4 cock and
maintain a proper air gap above your fill cup at all times }:-)

On Fri, Mar 19, 2010 at 6:23 AM, Forest Wilson <[email protected]> wrote:
> Tom,
> For priming dry pipe valves I usually use one of the backflow test cocks,
> attach the hose and fill into the cup.
> Forest Wilson
> Cherokee Fire
>
> -----Original Message-----
> From: [email protected]
> [mailto:[email protected]] On Behalf Of Tom Duross
> Sent: Friday, March 19, 2010 8:43 AM
> To: [email protected]; [email protected]; [email protected]
> Subject: RE: dry system air leak
>
> I was on an earlier thread about finding leaks.  We had 2 fairly large dry
> systems installed in the mid 70's and spending a lot of time servicing them.
> I was going to try the scented oil method but even after flooding and
> hyro-ing them, we couldn't find everyone.  Some of the mains & risers were
> behind finish.  After finding leaks in both valve's trim assemblies and
> EOL's (good call Todd) and repairing them, all we could guess were buried
> grooved couplings.  I couldn't go and buy expensive detectors or listening
> devices.  We ended up replacing them with low diff. dry valves, 13 PSI of
> air instead of 45.
>
> I will add, we found lots of trapped sections of main, doubled the quantity
> of drum drips.  Plus, don't use a sight glass on the lower leg, they leak.
> I thought it might be a good idea, you could see water with a flashlight but
> with 2 kinds, brass and ci cross type, the both leaked air.  We did use
> longer sections of 2" in the drums where we could, just for more capacity.
>
> Has anyone ever installed a fill line for a traditional dry valve like the
> priming valves they have for the external reset dry and deluge valves?  Just
> a 1/2" or 1/4" below the gate off the boss and some flexible copper or hose
> for filling?  I looked at that priming valve on the low diff. dpv and
> thought it might work instead of ladling a coffee cup at a time out of a 5
> gallon bucket.
>
> Tom
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> For Technical Assistance, send an email to: [email protected]
>
> To Unsubscribe, send an email to:[email protected]
> (Put the word unsubscribe in the subject field)
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> For Technical Assistance, send an email to: [email protected]
>
> To Unsubscribe, send an email to:[email protected]
> (Put the word unsubscribe in the subject field)
>



-- 
Ron Greenman
Instructor
Fire Protection Engineering
Bates Technical College
Tacoma, WA

Member:
SFPE, ASCET, NFPA, AFSA, NFSA AFAA, NIBS, WSAFM, WFC
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to