It seems to me that you can meet 11.1.2 without meeting room design
requirements, as you state no mention of automatic closing doors or rated
walls.
I believe that what 11.1.2 is stating is that if the heat from a fire in
that 600SF room will set off the heads in that room, without heat activating
the sprinklers in the adj. area, then what we expect to happen is for the
fire to be contained to the room of origin if that room is properly
protected.

Thom McMahon, SET
Firetech, Inc.
2560 Copper Ridge Dr
P.O. Box 882136
Steamboat Springs, CO 80488
Tel:  970-879-7952
Fax: 970-879-7926



-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Richardson, R
Sent: Monday, March 22, 2010 11:55 AM
To: [email protected]
Subject: RE: Room Design vs. Adjacent Hazards

It does meet 11.1.2 (subject to a massive interpretation as to what
constitutes adequate separation), but does not meet room design because the
wall is not fire rated, the doors in the wall are not self-closing and they
are not including two heads outside the OH area as required by room design.

Rich

-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Thom McMahon
Sent: Monday, March 22, 2010 10:42
To: [email protected]
Subject: RE: Room Design vs. Adjacent Hazards

Rich:

How does your 600 Sf OH space not meet the requirements of 11.1.2(2)? And
still qualify for room design?

Thom McMahon, SET
Firetech, Inc.
2560 Copper Ridge Dr
P.O. Box 882136
Steamboat Springs, CO 80488
Tel:  970-879-7952
Fax: 970-879-7926



-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Richardson, R
Sent: Monday, March 22, 2010 11:33 AM
To: [email protected]
Subject: Room Design vs. Adjacent Hazards

In reference to 2007 NFPA 13 section 11.1.2 Adjacent Hazards, is this
considered a stand-alone code section or does one still have to meet all of
the room design criteria.  

The question is relevant to a situation where a small ordinary hazard space
is app. 600 sq.ft. adjacent to a light hazard space and they are using
11.1.2.  

It seems that section 11.1.2. essentially makes the room design irrelevant.


Thanks,

Rich Richardson
Seattle Fire Department
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to