If the existing sprinkler(s) within the room comply with 
2007/13-8.6.5.1.2(b)-obstructions Against Walls (SSU/SSP) (assuming no res. 
sprinklers were used) there should be no issue.  Need to know the type of 
sprinkler and the depth of the space previously occupied by the wardrobe below 
header.

Dan

-----Original Message-----
From: [email protected] 
[mailto:[email protected]] On Behalf Of Greg Schulze
Sent: Tuesday, March 23, 2010 10:20 AM
To: [email protected]
Subject: Small alcove protection in room

I have several patient rooms in a nursing home that  had a wardrobe unit
recessed in the wall and was 7 feet high.  A 12" header was placed from the
top of the wardrobe unit to the existing 8  foot ceiling for cosmetic
reasons creating a concealed noncombustible space above the units.   The
units  were removed leaving behind a 12" deep header from the ceiling.  The
fire official wants a sprinkler added in the space created by the removal of
the units, covering approx. 4 sq ft.   The existing sprinklers provide
coverage into the newly created alcove from the room.  Is there a specific
code reference that allows me to consider the sprinklers in the room as
providing coverage of this space or should I advise my customer he needs to
remove either the 12" headers,  close off this space or add the additional
heads?  Any help is appreciated.





Greg Schulze

Project Designer



TDK Enterprises Inc.

ARK Protective Services - Absolute Security Unlimited

9 Florence Ave. Carneys Point, NJ 08069

Phone 856-299-2900

Fax 856-299-2959

Mobile: 856-889-9498

Email:  <mailto:[email protected]> [email protected]



_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

--
ExchangeDefender Message Security: Click below to verify authenticity
http://www.exchangedefender.com/verify.asp?id=o2NHV7lf016835&[email protected]

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to