It needs clarification. I have been factory trained and issued a certificate of 
competency for fire pumps and firetrol controllers. 
So the manufacturer says I'm competent but this commentary states only licensed 
electricians are qualified. 
We utilize OSHA Consultation Services and properly address safety hazards 
associated with fire pumps and controllers. 


Forest Wilson 
Cherokee Fire 

Sent from my Verizon Wireless Phone

----- Reply message -----
From: "John Drucker" <[email protected]>
Date: Wed, Apr 7, 2010 11:24 AM
Subject: NFPA 25 QUALIFICATIONS FOR WORKING ON FIRE PUMP
To: <[email protected]>


Perhaps the assumption stems from the following language in NFPA-20,
albeit less the "licensed" part;

1999 - 11-2.1 All electric wiring to the fire pump motor(s), including
control (multiple pumps) interwiring, emergency power supply, and jockey
pump, shall be completed and checked by the electrical contractor prior
to the initial startup and acceptance
test.

2003 - 14.2.3 All electric wiring to the fire pump motor(s), including
control (multiple pumps) interwiring, normal power supply, alternate
power supply where provided, and jockey pump, shall be completed and
checked by the electrical contractor prior to the initial startup and
acceptance test.

2007 - 14.2.3 All electric wiring to the fire pump motor(s), including
control (multiple pumps) interwiring, normal power supply, alternate
power supply where provided, and jockey pump, shall be completed and
checked by the electrical contractor prior to the initial startup and
acceptance test.

2010 - 14.2.3 Pump Room Electrical Wiring. All electric wiring to the
fire pump motor(s), including control (multiple pumps)
interwiring,normal power supply, alternate power supply where provided,
and jockey pump, shall be completed and checked by the electrical
contractor prior to the initial startup and acceptance test.

Additionally, 2002 NFPA-20 "Form for Inspection, Testing and Maintenance
of Fire Pumps" does include the following language, albeit it's a sample
form located in the annex; Part 1 Owners Section: "Note to owner:
Periodic tests of transfer switches and emergency generators are to be
performed in accordance with NFPA 110 by a qualified electrical
contractor."

But my bet its rooted in this; 2008 NFPA-25; 4.9* Electrical Safety.
Legally required precautions shall be taken when testing or maintaining
electric controllers for
motor-driven fire pumps."

John Drucker Jr CET
Fire Protection Subcode Official
Fire/Building/Electrical Inspector
Borough of Red Bank, NJ 

-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Roland
Huggins
Sent: Wednesday, April 07, 2010 10:36 AM
To: [email protected]
Subject: Re: NFPA 25 QUALIFICATIONS FOR WORKING ON FIRE PUMP 

I have never heard this even suggested at the NFPA 25 meetings.  Since
the text in 25 does not even suggest it, I would put it down as an
over-zealous editor in the Handbook.  I will pursue clarification of
this with NFPA for the next edition of the Handbook (which we just
finished working on).

Roland

On Apr 6, 2010, at 3:57 PM, [email protected] wrote:

> NFPA 25-8.3.3.6 Handbook commentary states that a licensed electrician

> should perform work near fire pumps.
> Is the Committee trying to establish that only licensed electricians 
> should perform work on or near controllers, or that an electrician 
> should always be present?
> Can someone please clarify what the commentary is implying or stating?
>
> Forest Wilson
> Cherokee Fire
>
> Sent from my Verizon Wireless Phone
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> For Technical Assistance, send an email to: [email protected]
>
> To Unsubscribe, send an email 
> to:[email protected]
> (Put the word unsubscribe in the subject field)
>

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email
to:[email protected]
(Put the word unsubscribe in the subject field)


CONFIDENTIAL AND PROPRIETARY:
This email message is intended only for the use of the individual or entity to 
which it is addressed and may contain information that is privileged and 
confidential, nor is it, unless specifically stated, intended to be relied upon 
by any person or persons other than the individual or entity named above and no 
warranties or representations are made or intended to persons or entities not 
named above.  If the reader is not the intended recipient, you are hereby 
notified that any dissemination, distribution or copying of this communication 
is strictly prohibited.  If you have received this communication in error, 
please notify us immediately by telephone, return this message to the address 
above and delete all copies.  Thank you.

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)