I think the problem with dry grids is, once the valve trips, the water goes through all the lines, (pushing all the air), not down a single main, and just a few branch lines?
-----Original Message----- From: Ron Greenman [mailto:[email protected]] Sent: Friday, April 09, 2010 11:24 AM To: [email protected] Subject: Re: dry grid question If I'm understanding correctly you essentially have a tree with a riser feeding a cros-main feeding multiple individual branch lines and then that you've brought another riser (feed main) to the opposite end of the cross-main and tied it in. I'd say this is a loop since you're you're not using the branch lines as feeder pipe to the parallel cross-mains. In fact I'll bet you plan on gang-draining the branch lines which would look more like a grid. I think the key here is that the design heads aren't floating somewhere in the middle of this arrangement and relying on all the branch lines as feeder. Imagine a crazy architect (not hard) that gave you a 0'3" deep x something like 2'0" wide cavity to put a 4" riser, and wouldn't consider a bump out for chase, but you had an unfinished space below and were going into an attic. Couldn't you manifold the riser and bring up two 2 1/2" pipes (presuming those were enough to carry the required flow) and then manifold them back together? Just has to calc. I see this pretty much the same way but I'm sure I'm wrong here so let's hear from some others. I'd like to see how this all plays out. On Fri, Apr 9, 2010 at 7:32 AM, Todd Williams <[email protected]> wrote: > I am working on an attic sprinkler system and have a question on pipe > arrangement. The building is 250 x 58 and the attic is unheated. I > have a single row of attic sprinklers down the peak and some APs in > the dormers. My calc area is 7 BB1s and 2 APs, per the listing. > Hydraulics are tight, so I am looking to come up with a more > efficient pipe layout. What I came up with is a continuous line at > the peak running down the center, fed near each end by a cross main > which connects to the central dry system riser. My question is does > this violate the prohibition of gridded dry systems? NFPA 13 defines > a grid as two parallel cross mains connecting multiple branch lines. > In this case, I have a two cross mains connecting a single branch > line. However, a looped system, which is allowed, specifically states > that branch lines not be connected. Am I OK with this layout? > > Todd G. Williams, PE > Fire Protection Design/Consulting > Stonington, CT > 860.535.2080 > www.fpdc.com > > > _______________________________________________ > Sprinklerforum mailing list > [email protected] > http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum > > For Technical Assistance, send an email to: [email protected] > > To Unsubscribe, send an email to:[email protected] > (Put the word unsubscribe in the subject field) > -- Ron Greenman Instructor Fire Protection Engineering Bates Technical College Tacoma, WA Member: SFPE, ASCET, NFPA, AFSA, NFSA AFAA, NIBS, WSAFM, WFC _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [email protected] To Unsubscribe, send an email to:[email protected] (Put the word unsubscribe in the subject field) _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [email protected] To Unsubscribe, send an email to:[email protected] (Put the word unsubscribe in the subject field)