A single loop is permitted. At least it used to be, haven't checked the new codes. More than one loop can be considered a grid, and not permitted. What I have done in the past is run a main, (say 4"), below the peak at a low level, then rise up with branch lines (say 2") to the peak and supply 3 or 4 BB heads per branch line. (the number depending on the water supply). The branch lines at the peak are not connected. The 4" at the low level can feed the AP's in the dormers without trapping problems. If need be, you can supply this main at both ends to form a loop.
Tony -----Original Message----- From: [email protected] [mailto:[email protected]] On Behalf Of Todd Williams Sent: April 9, 2010 8:33 AM To: [email protected] Subject: dry grid question I am working on an attic sprinkler system and have a question on pipe arrangement. The building is 250 x 58 and the attic is unheated. I have a single row of attic sprinklers down the peak and some APs in the dormers. My calc area is 7 BB1s and 2 APs, per the listing. Hydraulics are tight, so I am looking to come up with a more efficient pipe layout. What I came up with is a continuous line at the peak running down the center, fed near each end by a cross main which connects to the central dry system riser. My question is does this violate the prohibition of gridded dry systems? NFPA 13 defines a grid as two parallel cross mains connecting multiple branch lines. In this case, I have a two cross mains connecting a single branch line. However, a looped system, which is allowed, specifically states that branch lines not be connected. Am I OK with this layout? Todd G. Williams, PE Fire Protection Design/Consulting Stonington, CT 860.535.2080 www.fpdc.com _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [email protected] To Unsubscribe, send an email to:[email protected] (Put the word unsubscribe in the subject field) _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [email protected] To Unsubscribe, send an email to:[email protected] (Put the word unsubscribe in the subject field)