If you are participating in the thread regarding OHIII pls ignore this til Monday!
Does anyone have any info on the following: Water pressure against glass - specifically, if you calc 40 nozzles for glazing protection at 7 psi minimum and only one deluge system activates so there is 168 psi static pressure available and the smallest system is only 5 nozzles.....at what point does it become a concern? Operating temp of Dry Pilot Heads Outside for the same systems - Outside so the pilot heads should be of the intermediate temp classification (they are under a soffit for the most part): a) Would relatively high pressure and a possible glass temp of over 200 degress be a problem? b) when the pilot heads are NOT under a soffit I believe they need to be high temp - same question. Have a great weekend! Greg McGahan Living Water Fire Protection (850) 937.1850 | Fax (850) 937.1852 | Cell (850) 554.3231 -----Original Message----- From: [email protected] [mailto:[email protected]] On Behalf Of Law, Kevin W Sent: Friday, April 09, 2010 4:54 PM To: [email protected] Subject: RE: OHIII You can really tell by the chatter that it is late on a Friday afternoon and no one is really interested in doing anymore real work for the day. :O] Kevin Law, PE Bechtel National, Inc. Waste Treatment Project Fire Protection Engineering Work (509) 371-3280 Cell (509) 531-5715 -----Original Message----- From: [email protected] [mailto:[email protected]] On Behalf Of Todd Williams Sent: Friday, April 09, 2010 2:23 PM To: [email protected] Subject: RE: OHIII Brilliant!! At 05:14 PM 4/9/2010, you wrote: >In the beginning there was darkness....business was a little slow.... >:) > >Matt Grisé PE*, LEED AP >Sales Engineer >Alliance Fire Protection >*Licensed in KS & MO > >913.888.0647 ph >913.888.0618 f >913.927.0222 cell >www. AFPsprink.com > > >-----Original Message----- >From: [email protected] >[mailto:[email protected]] On Behalf Of >A.P.Silva >Sent: Monday, May 10, 2010 3:14 PM >To: [email protected] >Subject: RE: OHIII > >Designing sprinklers for inside caves, and drafting on rock walls is >another story. Then doing hydraulic calculations on the abacus, or did >that come later? I'd better stop now, or will really be showing my age. > >Tony > >-----Original Message----- >From: [email protected] >[mailto:[email protected]] On Behalf Of Matt >Grise >Sent: April 9, 2010 3:00 PM >To: '[email protected]' >Subject: RE: OHIII > >At least we no longer have to budget time for fighting dinosaurs! > >Matt Grisé PE*, LEED AP >Sales Engineer >Alliance Fire Protection >*Licensed in KS & MO > >913.888.0647 ph >913.888.0618 f >913.927.0222 cell >www. AFPsprink.com > > >-----Original Message----- >From: [email protected] >[mailto:[email protected]] On Behalf Of >A.P.Silva >Sent: Monday, May 10, 2010 2:56 PM >To: [email protected] >Subject: RE: OHIII > >Wait another 20 years. There won't be any piping. Each sprinkler head >will have its own compressed water supply. Wait, wasn't that how it was >done ages ago? It's Friday. > >Tony > >-----Original Message----- >From: [email protected] >[mailto:[email protected]] On Behalf Of John >Drucker >Sent: April 9, 2010 2:49 PM >To: [email protected] >Subject: RE: OHIII > >These young guys have it made, vic fittings, weldolets, flex drops and >plastic pipe !. When I was eager and young we screwed 6" 40 with chain >wrenches and installed fittings where every outlet had to go. One day >someone came along with a roustabout and later cut grooved 40 on the >risers and crosses and we just stared at it. Oh the days of old......... > >John > >-----Original Message----- >From: [email protected] >[mailto:[email protected]] On Behalf Of Roland >Huggins >Sent: Friday, April 09, 2010 4:39 PM >To: [email protected] >Subject: Re: OHIII > > By saying it was ONLY 19 years ago, it doesn't sound like something >coming from someone that is Young. I just wish that I could qualify >for the Wise Old timer moniker. Guess I'll settle for Cantankerous, >old timer or maybe just old. > >Roland > >On Apr 9, 2010, at 1:22 PM, Ben Young wrote: > > > Well if it makes you guys feel any better, they still show the old > > curves in chapter 11 of the 13 handbook. Besides, it was only 1991 > > when they changed them! > > > > Benjamin Young > >_______________________________________________ >Sprinklerforum mailing list >[email protected] >http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum > >For Technical Assistance, send an email to: [email protected] > >To Unsubscribe, send an email >to:[email protected] >(Put the word unsubscribe in the subject field) > > >_______________________________________________ >Sprinklerforum mailing list >[email protected] >http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum > >For Technical Assistance, send an email to: [email protected] > >To Unsubscribe, send an email >to:[email protected] >(Put the word unsubscribe in the subject field) > >_______________________________________________ >Sprinklerforum mailing list >[email protected] >http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum > >For Technical Assistance, send an email to: [email protected] > >To Unsubscribe, send an email >to:[email protected] >(Put the word unsubscribe in the subject field) >_______________________________________________ >Sprinklerforum mailing list >[email protected] >http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum > >For Technical Assistance, send an email to: [email protected] > >To Unsubscribe, send an email >to:[email protected] >(Put the word unsubscribe in the subject field) > >_______________________________________________ >Sprinklerforum mailing list >[email protected] >http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum > >For Technical Assistance, send an email to: [email protected] > >To Unsubscribe, send an email >to:[email protected] >(Put the word unsubscribe in the subject field) >_______________________________________________ >Sprinklerforum mailing list >[email protected] >http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum > >For Technical Assistance, send an email to: [email protected] > >To Unsubscribe, send an email >to:[email protected] >(Put the word unsubscribe in the subject field) Todd G. Williams, PE Fire Protection Design/Consulting Stonington, CT 860.535.2080 www.fpdc.com _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [email protected] To Unsubscribe, send an email to:[email protected] (Put the word unsubscribe in the subject field) _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [email protected] To Unsubscribe, send an email to:[email protected] (Put the word unsubscribe in the subject field) _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [email protected] To Unsubscribe, send an email to:[email protected] (Put the word unsubscribe in the subject field)