Large pool fires (especially in tank farms-of-substantial-diameter)
are not de facto, "non-exposure threats".   A lower regard, but
not exclusively, can be held for fires in diked containment
areas.   Proximity of exposed tanks, without even considering
wind-aided plume tilt,  can make the exposed tanks and their
appurtenances vunerable.  This does not even consider the
possibilities of escalation from crude boilover.  Burn
down can take a couple of days for a full-surface fire in a
topped off tank; that is a lot of time to be exposing surrounding equipment.
Even burn down, let alone attack operations, warrants diligent
protection of tanks-and-appurtenances which are too close for comfort:
occassional-to-continual cooling is expected for equipment, depending
upon its proximity to the exposure.

If someone were designing for such exposure scenarios, I would
highly recommend not leaving this responsibility to someone who
looked up the answer in a standard, or even someone who is
intimately familiar with the process department of their refinery/storage
facility.  This is a specialized field requiring knowledge that few people
acquired, and the amount of misinformation is staggering...especially
considering the large-scale consequences.  It is fair to say that very
little
tactical efforts will make up for poor strategic decisions when dealing
with large pool fires.   A lot of large-diameter flammable/
combustible liquid tank-farms are over-exposed / underprotected, without
stakeholders realizing it.  This is definitely one area where we can get
burned,
but fatal.  Fire is highly non-linear, and at scales > 60 ft, the exposure
from these tank fires simply is not in the event horizon of most process,
mechanical,
civil, electrical engineers' consciousness.   For adequate suppression and
exposure protection, we should consult with professionals having a
successful
track record (there are sufficient professional without successful track
records
[no aspersions cast upon these debators] in this highly specialized and
not-well
understood arena) with hands-on extinguishment of large, full-surface
flammable/combustible liquid fires.

scot deal
excelsior fire
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to