I have a newly renovated building; in this building is a 22x18 hyperbaric chamber room. This room has two single hyperbaric chambers. According to NFPA 99 20.1.5.2, these would be Class B chambers (correct me if I'm wrong). Per 20.2.6 Class B & C chambers do not require a fire suppression system. Per 20.2.1.3 "The room or rooms housing Class B & Class C chambers shall be afforded sprinkler protection in accordance with 20.2.1.2." (That's the first time I have seen it put like that), 20.1.2 "A hydraulically calculated automatic wet pipe sprinkler system meeting the requirements of NFPA 13 shall be installed in the room housing a Class A chamber and in any ancillary equipment rooms."
So if I interpret that correctly we need a wet type system in the room only. Now 13 only calls out A type chambers (21.19) so would the system need to be light hazard per 5.2 Hospitals? Or is there other direction for this room I'm missing? Bobby Gillett Sr. Project Manager Key Fire Protection, Inc. (731) 424-0130 office (731) 424-9285 fax (731) 267-4853 cell <mailto:[email protected]> [email protected] _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [email protected] To Unsubscribe, send an email to:[email protected] (Put the word unsubscribe in the subject field)