I did check 99 and quoted it below so I get other interpretation. I only referenced 21 in 13 because it was the only reference to hyperbaric chambers and that was for A type, I have B type so I was asking since I have B type would the room be protected per light hazard as shown in 5.2 "hospitals" of NFPA 13
Bobby Gillett Sr. Project Manager Key Fire Protection, Inc. (731) 424-0130 office (731) 424-9285 fax (731) 267-4853 cell [email protected] -----Original Message----- From: [email protected] [mailto:[email protected]] On Behalf Of John Denhardt Sent: Tuesday, April 27, 2010 3:27 PM To: [email protected] Subject: RE: Hyperbaric Chamber/Chamber rooms Remember - Since you are quoting Chapter 21 of NFPA 13 all NFPA 13's technical committee is allowed to do by the Standards Council is to copy the information word for word from NFPA 99. You might want to see what NFPA 99 states to see if it offers more information. John John August Denhardt, P.E. Strickland Fire Protection Incorporated 5113 Berwyn Road College Park, Maryland 20740 Office Telephone Number: 301-474-1136 Mobile Telephone Number: 301-343-1457 FIRE SPRINKLERS SAVE LIVES -----Original Message----- From: [email protected] [mailto:[email protected]] On Behalf Of Bobby Gillett Sent: Tuesday, April 27, 2010 4:00 PM To: [email protected] Subject: Hyperbaric Chamber/Chamber rooms I have a newly renovated building; in this building is a 22x18 hyperbaric chamber room. This room has two single hyperbaric chambers. According to NFPA 99 20.1.5.2, these would be Class B chambers (correct me if I'm wrong). Per 20.2.6 Class B & C chambers do not require a fire suppression system. Per 20.2.1.3 "The room or rooms housing Class B & Class C chambers shall be afforded sprinkler protection in accordance with 20.2.1.2." (That's the first time I have seen it put like that), 20.1.2 "A hydraulically calculated automatic wet pipe sprinkler system meeting the requirements of NFPA 13 shall be installed in the room housing a Class A chamber and in any ancillary equipment rooms." So if I interpret that correctly we need a wet type system in the room only. Now 13 only calls out A type chambers (21.19) so would the system need to be light hazard per 5.2 Hospitals? Or is there other direction for this room I'm missing? Bobby Gillett Sr. Project Manager Key Fire Protection, Inc. (731) 424-0130 office (731) 424-9285 fax (731) 267-4853 cell <mailto:[email protected]> [email protected] _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [email protected] To Unsubscribe, send an email to:[email protected] (Put the word unsubscribe in the subject field) _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [email protected] To Unsubscribe, send an email to:[email protected] (Put the word unsubscribe in the subject field) No virus found in this incoming message. Checked by AVG - www.avg.com Version: 9.0.814 / Virus Database: 271.1.1/2838 - Release Date: 04/27/10 01:27:00 _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [email protected] To Unsubscribe, send an email to:[email protected] (Put the word unsubscribe in the subject field)