There are also a lot of instances where you SHOULD (read must if not
shall) mix temperatures such as around heating appliances. If there is
a reason for doing so I can think of nothing that prohibits it. Random
mixing 'cause you have a lot of 365ers in the truck is another story.

On Thu, May 6, 2010 at 10:58 AM, Reed Roisum <[email protected]> wrote:
> Chris,
>
> The commentary in A.6.2.5 ('07 ed.) says that sprinklers with the same temp. 
> rating SHOULD be used in a given AREA, unless otherwise specified by 8.3.2.
>
> The word 'compartment' is used earlier in this 'blue' print but I would 
> venture to say that the 18" beam does not separate this space into two 
> compartments unless the opening is less than 8 ft. (3.3.5).  So I would say 
> that you SHOULDN'T do this based on 13...
>
> But then again, you are looking for the bare minimum and I don't see any 
> "thou shalt nots" and it might be fair to say that you most likely wouldn't 
> see skipping due to the arrangement you described??  I dunno...do what you 
> want. :)
>
>
> Reed A. Roisum, CET
>
> Engineering Technician
> Ulteig, Engineers, Inc.
>
>
> Direct: (701)280-8580
>
>
>
> -----Original Message-----
> From: [email protected] 
> [mailto:[email protected]] On Behalf Of Chris Cahill
> Sent: Thursday, May 06, 2010 12:25 PM
> To: [email protected]
> Subject: Sprinkler temp
>
> Can you mix ordinary and high temp sprinklers in an ordinary hazard room?
> Does it make a difference if there is an 18" beam between them?  I see the
> SR v QR clearly says no. But I don't see the same clear statement in the
> temperature portion.
>
>
>
> I'm not suggesting it's a good idea, just what is minimally legal per 13.
> It's a big room of ministorage lockers that don't go to the clg.  One bay
> was added and the SC used ordinary heads.  The existing is high temp from
> the day it used to be HPS.  There is an 18" beam.  There are like 100 -
> 286's and maybe 10 - 165's.
>
>
>
> Chris Cahill, P.E.
>
> Fire Protection Engineer
>
> Sentry Fire Protection, Inc.
>
>
>
> 763-658-4483
>
> 763-658-4921 fax
>
>
>
> Email: [email protected]
>
>
>
> Mail: P.O. Box 69
>
>        Waverly, MN 55390
>
>
>
> Location: 4439 Hwy 12 SW
>
>              Waverly, MN 55390
>
>
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> For Technical Assistance, send an email to: [email protected]
>
> To Unsubscribe, send an email to:[email protected]
> (Put the word unsubscribe in the subject field)
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> For Technical Assistance, send an email to: [email protected]
>
> To Unsubscribe, send an email to:[email protected]
> (Put the word unsubscribe in the subject field)
>



-- 
Ron Greenman
Instructor
Fire Protection Engineering
Bates Technical College
Tacoma, WA

Member:
AFT WA 4184/AFL-CIO, SFPE, ASCET, NFPA, AFSA, NFSA AFAA, NIBS, WSAFM, WFC
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to