Any takers out there for this ANG ETL related question? Per ETL 02-15 para A1.4.3.10, "At least one arrester will be provided for each pump and each must be listed/approved as a surge arrester for fire protection piping, with a volume of not less than 100 gal and a rated working pressure of not less than 250 psi. Provide each arrester with an indicating valve to isolate it from the system." We are having a little argument here in the office as to whether the intent here is to require separate surge arresters for each pump or whether the combined required capacities for all surge arresters can be combined into one large arrester.
Example: 3 pumps = 3 - 100 gal surge arresters Or 3 pumps = 1 - 300 gal surge arrester Thank you, Ryan L. Hinson, EIT, NICET III Fire Protection Engineer, Aviation & Facilities Group Burns & McDonnell Minneapolis-St. Paul Office 8201 Norman Center Drive, Suite 300 Bloomington, MN 55437 Direct: 952-656-6003 Ext 3662 Fax: 952-229-2923 [email protected] www.burnsmcd.com<BLOCKED::www.burnsmcd.com> Proud recipient of PSMJ's Premier Award for Client Satisfaction _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [email protected] To Unsubscribe, send an email to:[email protected] (Put the word unsubscribe in the subject field)