I think it is 3 pumps 3 arresters. The main line of reasoning here is,
it's the government and they are buying something that is useless and
unnecessary so more must be better. It's like when the pump is in the
room with the riser manifold. It's a 100 gallon on the pump and a 10
gallon arrester on each riser, not a 150 gallon on five riser manifold
with pump.

Ron Fletcher
Aero Automatic
Phoenix, AZ

-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Hinson,
Ryan
Sent: Wednesday, May 26, 2010 3:02 PM
To: '[email protected]'
Subject: ETL Surge suppressor configuration

Any takers out there for this ANG ETL related question?

Per ETL 02-15 para A1.4.3.10, "At least one arrester will be provided
for each pump and each must be listed/approved as a surge arrester for
fire protection piping, with a volume of not less than 100 gal and a
rated working pressure of not less than 250 psi. Provide each arrester
with an indicating valve to isolate it from the system."  We are having
a little argument here in the office as to whether the intent here is to
require separate surge arresters for each pump or whether the combined
required capacities for all surge arresters can be combined into one
large arrester.

Example:

3 pumps = 3 - 100 gal surge arresters

Or

3 pumps = 1 - 300 gal surge arrester

Thank you,

Ryan L. Hinson, EIT, NICET III
Fire Protection Engineer, Aviation & Facilities Group
Burns & McDonnell
Minneapolis-St. Paul Office
8201 Norman Center Drive, Suite 300
Bloomington, MN 55437
Direct: 952-656-6003 Ext 3662
Fax: 952-229-2923
[email protected]
www.burnsmcd.com<BLOCKED::www.burnsmcd.com>


Proud recipient of PSMJ's Premier Award for Client Satisfaction

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email
to:[email protected]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to