Ron,
I did one of these at Mt Home AFB several years ago.  We were given the same
design criteria as you have been given.

Bob

-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Fletcher, Ron
Sent: Wednesday, May 26, 2010 3:30 PM
To: [email protected]
Subject: RE: Occupancy vs Hazard

It's a munitions maintenance facility for missiles. I suppose once the
mushroom cloud clears the type of sprinkler system wouldn't really matter.

Ron Fletcher
Aero Automatic
Phoenix, AZ

-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of
[email protected]
Sent: Wednesday, May 26, 2010 2:13 PM
To: [email protected]
Subject: RE: Occupancy vs Hazard

H-1 is a detonation hazard.  Fireworks, explosives, organic compounds, etc.
could all fall under that category.  But you would also need to consider
other materials used such as paper for casings of fireworks or plastics for
storage of peroxides, etc.   It's not a simple one point analysis.  So you
could actually have multiple NFPA 13 classification within the facility.


I've got an H-4, that's due to dust issues, no flammables or combustible
liquids present.  No fire threat from the process.  An EX classification
would be gross overkill and provide nothing except extra cost.  

The one problem with the Occupancy listings in NFPA 13 is that when used by
a novice, they can result in a wrong conclusion.  This case in point.  The
EOR probably looked at OHII for chemical plants and said BINGO!  Now I'm not
saying that his conclusion is wrong, it might be dead on.  

Unfortunately he could be way off if he did not look at everything going
into this plant, the locations, the quantities, use, storage, handling,
compatibilities, etc....

Hazardous occupancy classification for fire protection systems is one area
that probably has more screw-ups than any other due to the complexity of the
analysis and lack of black and white direction.  If the facility is not in
the list in A.5.2 then most just make a wild guess based on the first thing
the owner tells them.  

Industrial occupancies need an experienced "engineer" who can make the
determination because there are cases when NFPA 13 is NOT the applicable
primary Standard.  Unfortunately there are many who don't realize that NFPA
has anything other than the 13 Standard.  


Craig L. Prahl, CET   
Fire Protection Specialist
Mechanical Department
CH2MHILL
Lockwood Greene
1500 International Drive
Spartanburg, SC  29304-0491
Direct - 864.599.4102
Fax - 864.599.8439
[email protected]
http://www.ch2m.com 


-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Fletcher, Ron
Sent: Wednesday, May 26, 2010 4:53 PM
To: [email protected]
Subject: Occupancy vs Hazard

Is there a correlation between the IBC occupancy and NFPA #13 Hazard? I
have a set of plans where the building occupancy classification is H-1
and the EOR has specified OH-II for the sprinkler system. I have always
thought (maybe mistakenly) that any H occupancy would be EH-I minimum.

Ron Fletcher
Aero Automatic
Phoenix, AZ

No virus found in this outgoing message.
Checked by AVG - www.avg.com 
Version: 9.0.819 / Virus Database: 271.1.1/2899 - Release Date: 05/27/10
00:25:00

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to