well the walkway creates a problem, now it's an obstruction....so they have
movng ladders tor reach stuff...don't do a walkway, but your still looking
at a rack storage problem with solid shelves...check chap 12  ..specifically
12.2.2.1.5.3 & 12.2.2.1.6...02 edition

On Tue, Jun 22, 2010 at 1:07 PM, Dewayne Martinez <[email protected]> wrote:

> Storage to ceiling clearance = 4'-0"
> 30" aisle, 24" solid metal shelf depth, 24in apart vertically
> Class II commodity, non encapsulated, in metal bins (4 sided only-no
> top)
>
> I didn't think this met the definition of rack storage that is why I did
> not look there.
>
> -----Original Message-----
> From: [email protected]
> [mailto:[email protected]] On Behalf Of tom
> poisal
> Sent: Tuesday, June 22, 2010 10:44 AM
> To: [email protected]
> Subject: Re: shelf storage-NFPA 13 (07ed)
>
> Then you are moving into racks and such...what is your ceiling
> clearance, aisle width, commodity, container, etc. ?
>
> On Tue, Jun 22, 2010 at 10:57 AM, Dewayne Martinez
> <[email protected]>wrote:
>
> >    Is there any way to have shelf storage greater than 15ft?
> > It appears that the cutoff of 15ft per 14.2.1 (2).
> > I have a customer that wants 18ft of shelf storage with an arrangement
>
> > like 14.5 with a walkway at 12ft.
> >    What about putting plywood on the walkway and calling it 12ft of
> > storage on each level?
> > Thanks,
> > Dewayne
> > _______________________________________________
> > Sprinklerforum mailing list
> > [email protected]
> > http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
> >
> > For Technical Assistance, send an email to: [email protected]
> >
> > To Unsubscribe, send an email
> > to:[email protected]<to%[email protected]>
> <to%3ASprinklerforum-reques
> > [email protected]> (Put the word unsubscribe in the subject field)
> >
>
>
>
> --
> Tom Poisal, CET
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> For Technical Assistance, send an email to: [email protected]
>
> To Unsubscribe, send an email
> to:[email protected]<to%[email protected]>
> (Put the word unsubscribe in the subject field)
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> For Technical Assistance, send an email to: [email protected]
>
> To Unsubscribe, send an email 
> to:[email protected]<to%[email protected]>
> (Put the word unsubscribe in the subject field)
>



-- 
Tom Poisal, CET
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)