Reliability, listings, engineering and limited demand all factor into
the price.

Neither UL nor FM had a standard for air vents used on fire sprinkler
mains and branch lines. The only standard was for fire pumps.

Potter commissioned and paid UL to write a standard for vents for fire
sprinkler mains and branchlines, UL2573. The vents that were listed and
approved for fire pumps do not meet the UL standard for branch line
vents.

We spent over 2 years testing and researching vents until we found one
that would meet the requirements and then another year for the actual
approval process. We just received UL listing for the only vent approved
for branch lines. 

FM still does not have a standard for this, they still only approve for
use on fire pumps despite what some other company may advertise. Potter
is trying to get FM to also create a standard for branchlines but they
have not.

It's going to take a long time and a lot of sales to recoup our expenses
on this and I am reminded of that frequently by the people above me.

This is not an advertisement; I'm just answering a question.

Regards,

mike

Mike Henke CET
Sprinkler Product Manager
1-800-325-3936
314-595-6740 Direct
www.pottersignal.com
 
-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Matthew
J. Willis
Sent: Thursday, June 24, 2010 10:09 AM
To: [email protected]
Subject: RE: Automatic air release


>The device looks
> >pretty simple why so expensive? Reliability?
 

 

Listing?

Matthew J. Willis, CET
Automatic Fire Sprinklers
Norred Fire Systems L.L.C.
318-387-1134 Voice
318-816-1087 Mobile
318-387-1163 Facsimile
[email protected]

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email
to:[email protected]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to