The guy who specified the 15 fps; where is his thumb?


At 02:42 PM 6/25/2010, you wrote:
>NCDOI has a velocity limit in their standards, where it comes from, 
>who knows. Potter flow switches have a maximum surge of 18fps on the 
>VSR models. Is maximum surge the same has velocity?
>
>Thanks,
>Eric Tysinger CET
>NICET III - 108988
>Designer
>Wayne Automatic Fire Sprinklers, Inc.
>4370 Motorsport Drive
>Concord, NC 28027
>p: (704)782-3032 x1751
>f: (704)795-6838
>C: (239)633-9703
>
>
>-----Original Message-----
>From: [email protected] 
>[mailto:[email protected]] On Behalf Of Vince Sabolik
>Sent: Friday, June 25, 2010 2:33 PM
>To: [email protected]; [email protected]
>Subject: Re: limits on velocity
>
>I've run into a lot of other thumbs too, but was always taught
>16-32 fps since shortly after they invented water.
>
>At 02:27 PM 6/25/2010, you wrote:
> >The question was asked because a specifying engineer is requiring 15
> >fps on all pipes - including existing piping for a 6 story retrofit.
> >The existing system calculations indicate velocities of 34 fps.  :-)
>
>Vince Sabolik
>Christi Fire Protection, Inc.
>11351 Pearl Road
>Strongsville, Ohio 44136
>
>T 440 572-7730  F 440 572-7719  Email:
><mailto:[email protected]>[email protected]
>
>_______________________________________________
>Sprinklerforum mailing list
>[email protected]
>http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
>For Technical Assistance, send an email to: [email protected]
>
>To Unsubscribe, send an email to:[email protected]
>(Put the word unsubscribe in the subject field)
>_______________________________________________
>Sprinklerforum mailing list
>[email protected]
>http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
>For Technical Assistance, send an email to: [email protected]
>
>To Unsubscribe, send an email to:[email protected]
>(Put the word unsubscribe in the subject field)

Todd G. Williams, PE
Fire Protection Design/Consulting
Stonington, CT
860.535.2080
www.fpdc.com

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to