Be careful not to mount sprinklers so climber can grab them.



At 01:39 PM 7/2/2010, you wrote:
>Trying to paint this picture with text.
>
>
>
>I have an 18'-6" wide x 40' long rock wall floor plan, ceiling is an all
>glass skylight starting at 42' to 46' (about 19' along the slope) with the
>rock wall against the low side.  The rock wall is 40' tall for 1/3, 13' tall
>middle 1/3, 37' tall for 1/3.  At the floor, the wall varies on width
>extending out to about 9' at the top creating an overhang anywhere from
>4'-9'.  The belay points at the top have a 6" to 12" lip extending back over
>the wall (covered).  The tops of the two high areas are open, minus the
>overhangs.  The rock wall is a fiberglass over a metal lathe, construction
>of the wall is a type IIB.  There are access panels and access ladders in
>the space behind the wall so storage behind the wall is for certain.
>
>
>
>So, the plan is to have EC sidewalls at the high side of the skylight
>spraying down the slope.  The top of the walls are greater than 18" below
>the glass (almost 4') where they occur so they are not floor mounted
>obstructions per NFPA. We will have uprights beneath the 13' level as this
>is one large shelf to continue up the other 2 walls.
>
>
>
>My question is can I assume that the spray will both extend over and
>into/down the cavity created by the wall (behind) and also spray to the
>floor beneath the overhang created by the wall as it extends past vertical
>(the 4-9' distance)?
>
>
>
>I cannot use SC-HSW because the floor area will not be covered and it would
>require a 2nd line, and would definitely be an obstruction for the overhang.
>Pendents are out because the skylight steel will not support the piping and
>the overhang again and the Arch is having a conniption about the pipe where
>we can install it.
>
>
>
>It looks something like this..the EC sidewall would be to the lower right
>side spraying down and towards the wall
>
>http://eldowalls.com/wp-content/uploads/2008/05/modgeckoxlphantom-web.jpg
>
>
>
>Happy 4th!
>
>
>
>D
>
>_______________________________________________
>Sprinklerforum mailing list
>[email protected]
>http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
>For Technical Assistance, send an email to: [email protected]
>
>To Unsubscribe, send an email to:[email protected]
>(Put the word unsubscribe in the subject field)

Todd G. Williams, PE
Fire Protection Design/Consulting
Stonington, CT
860.535.2080
www.fpdc.com

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to