Eric,

NJ resolved that "problem", at least in residential by way of the
residential site improvement standard and commercially by way of the 2006
IFC/NJ.

http://www.nj.gov/dca/divisions/codes/codreg/pdf_regs/njac_5_21.pdf

http://www2.iccsafe.org/states/06NewJerseyFire/

John Drucker, CET
Fire Protection Subcode Official 
Fire/Building/Electrical Inspector
Fire Marshals Office
Borough of Red Bank, NJ


-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Eric Tysinger
Sent: Wednesday, July 14, 2010 3:55 PM
To: [email protected]
Subject: RE: hydrant spacing

When I had to deal with this in South Florida, it was always a
jurisdictional call. They all wanted something different depending on what
hose was carried on the trucks. Although 300 was the most common, additional
hydrants were often added to comply with their FDC to Hydrant spacings. 

Thanks,
Eric Tysinger CET
NICET III - 108988
Designer
Wayne Automatic Fire Sprinklers, Inc.
4370 Motorsport Drive
Concord, NC 28027
p: (704)782-3032 x1751
f: (704)795-6838
C: (239)633-9703


-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of
[email protected]
Sent: Wednesday, July 14, 2010 3:43 PM
To: [email protected]
Subject: Re: hydrant spacing

Tom,

Don't know if this has been answered.  IFC addresses this to a certain
extent.  I'm paraphrasing probably more than I should, but for example,
IFC-2006, 508.5.1 addresses the placement of hydrants for fire service use.
Essentially, a portion of a building or facility is required to be within
600 ft. of a hydrant as measured around the building.  400 ft. for
non-sprinklered.

Regards,



James L (Jim) Roberts, PE/SET| FLUOR | Principal Fire Protection Engineer -
Central Engineering | [email protected] | IODC 20.5149 | O
+1.864.281.5149 | www.fluor.com




















|---------+---------------------------------------->
|         |            tom poisal                  |
|         |            <[email protected]>        |
|         |            Sent by:                    |
|         |            sprinklerforum-boun...@fires|
|         |            prinkler.org                |
|         |            07/13/2010 05:02 PM         |
|         |            Please respond to           |
|         |            sprinklerforum              |
|---------+---------------------------------------->
 
>---------------------------------------------------------------------------
------------------------------------------|
  |
|
  |
|
  |
To|
  |        [email protected]
|
  |
cc|
  |
|
  |
Subject|
  |        Re:
|
  |
|
  |
|
  |
|
  |
|
  |
|
  |
|
 
>---------------------------------------------------------------------------
------------------------------------------|




AS an an aside I can't find what a required distance between fire hydrants
is, NFPA only says up to AHJ and FM is 300'

On Tue, Jul 13, 2010 at 4:58 PM, Firestone, James <
[email protected]> wrote:

> Dear Geir
>
> The New Zealand Fire Service has published a Code of Practice for
Fighting
> Water Supply (NZS PAS 4509:2008) - which can be freely downloaded from
our
> website
>
>
>
http://www.fire.org.nz/Business-Fire-Safety/Building-Design/Pages/Fire-safet
y-design.aspx

>
> Essentially there are two approaches you can take in this COP. A 
> prescriptive approach using Tables. Table 1 matches Building type/size 
> to
a
> water classification, while Table 2 stipulates the required fire 
> fighting water for this classification.
>
> Or you can use a fire engineering approach and match the (energy)
quenching
> efficiency of water to the size of the fire that the fire fighters 
> would
be
> faced with upon arrival. I have simplified this a lot just to get 
> across
the
> main idea.
>
> Basically in answer to your question we want to encourage building 
> owners to put the resource (water) where the risk is (which is within 
> the building)! Thus the recognised advance of a sprinkler system which
catches
> the fire whilst still small.
>
> So as a recognised trade-off, if a structure is sprinkler protected 
> (and just using the prescriptive method of the COP), then it only 
> requires an additional 25L/s fire fighting water.
>
> So the volume of (fire) water supplied to the building MUST be the 
> amount required for the sprinkler and the (operational) fire fighting 
> simultaneously. However as a caveat to this, if sprinklers are 
> installed
we
> do lend ourselves to negotiation on potentially allowing increased
hydrant
> distances, slightly reduced volumes (dependent upon risk, proximity to 
> a fire station, ease of fire fighting access around building, climatic 
> conditions, exposure protection requirements, etc.) where the building 
> is sited in a lower water serviced area than what is normally required 
> OR if the amount of water that is required to supply BOTH the 
> sprinkler system
and
> fire fighting is greater than that required for just fire fighting 
> (with
no
> sprinkler system present). The latter is a very rare case and usually
more
> an anomaly of the COP.
>
> Regards, James
>
>
> James Firestone
> Fire Engineer
> National Headquarters, NZ Fire Service P. O. Box 9346, Wellington, NZ 
> Level 6, 5-7 Willeston St, Wellington, NZ Cell - 0274858056, DDI (04) 
> 4708011 [email protected]
>
> Fires are fast - home sprinklers are faster - don't delay inquire 
> about
one
> today - see http://homesprinklers.fire.org.nz and keep yourself safe 
> and NZ green.
>
>
>
> -----Original Message-----
> From: [email protected] [mailto:
> [email protected]] On Behalf Of Geir Jensen
> Sent: Wednesday, 14 July 2010 01:59
> To: [email protected]
> Subject:
>
> On which conditions does sprinkler substitute fire brigade water flow 
> requirements?  Never?  Cannot figure out by NFPA 1 Ch 18 and NFPA 13.
> Sprinkler demand and hose demand are to be added, except for 50 % or 
> 75 % reduction as per NFPA 1 Ch 18?
>
> How does NFPA 13 "hose allowance" relate to "fire flow requirements 
> for buildings" (NFPA 1, 18.4)? Are they equal for a given sprinklered
structure?
>
> Does sprinkler protection have any influence on water supply duration 
> requirements?  Shall duration comply with NFPA 1 or NFPA 13 for
sprinklered
> structures? Are requirements to "hydrant water supply" and "fire flow 
> requirements for buildings" both influenced, if any at all?
>
> Please accept the above very basic questions. I am working on 
> guidelines for sprinkler trade offs. As guideline become 
> performance-based I need to know if your prescriptive standards 
> acknowledge sprinkler performance as
is,
> i.e. say reducing water supply requirements (flow and duration) to a
level
> sufficient for hose extinguishing of sprinkler controlled fires only.
>
> Geir
>
> Geir Jensen
> COWI Fire
> Technical Director
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> For Technical Assistance, send an email to: [email protected]
>
> To Unsubscribe, send an email
to:[email protected]<to%3asprinklerforum-requ...@fire
sprinkler.org>

> (Put the word unsubscribe in the subject field)
>
> ----------------------------------------------------------------
> This e-mail message has been scanned and cleared by MailMarshal
> ----------------------------------------------------------------
> ---------------------------------------------------------------
> This e-mail message has been scanned and cleared by MailMarshal
> ---------------------------------------------------------------
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> For Technical Assistance, send an email to: [email protected]
>
> To Unsubscribe, send an email
to:[email protected]<to%3asprinklerforum-requ...@fire
sprinkler.org>

> (Put the word unsubscribe in the subject field)
>



--
Tom Poisal, CET
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)
------------------------------------------------------------
The information transmitted is intended only for the person or entity to
which it is addressed and may contain proprietary, business-confidential
and/or privileged material.  
If you are not the intended recipient of this message you are hereby
notified that any use, review, retransmission, dissemination, distribution,
reproduction or any action taken in reliance upon this message is
prohibited. If you received this in error, please contact the sender and
delete the material from any computer.  

Any views expressed in this message are those of the individual sender and
may not necessarily reflect the views of the company.  
------------------------------------------------------------
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to