2006 IBC 1014.3 Exception 1.

Extends the common path of travel distance from 75ft to 125ft if
903.1.1.1 (NFPA-13) Sprinkler System.

Hope that helps,

John Drucker Jr CET
Fire Protection Subcode Official
Fire/Building/Electrical Inspector
Borough of Red Bank, NJ 
 

-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Steve
Leyton
Sent: Monday, July 19, 2010 1:07 PM
To: [email protected]
Subject: Egress travel distance - 13R - 13 upgrade?

Can anyone (Drucker) help me with this:

 

I have hazy recall of a provision in the building code that if egress
travel distance in a dwelling unit is more than a threshold distance
(100', I think) from the egress system, then the design has to be
upgraded to a full 13.  There are several of these little switches
buried in the I-code for multi-family residential, such as a 13 upgrade
that will allow unprotected openings to be tabulated for area as if they
were protected (704.8.1), but I can't find this one.   Or maybe I
imagined it?

 

Steve Leyton

PROTECTION DESIGN & CONSULTING

2851 Camino del Rio South, Suite 400

San Diego, CA 92108

-------------------------------------------------------------

Ph:      858.751.2930 - ext. 102

Fax:    858.751.2933

Cell:  619.972.5696

 

 

 

 

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email
to:[email protected]
(Put the word unsubscribe in the subject field)


CONFIDENTIAL AND PROPRIETARY:
This email message is intended only for the use of the individual or entity to 
which it is addressed and may contain information that is privileged and 
confidential, nor is it, unless specifically stated, intended to be relied upon 
by any person or persons other than the individual or entity named above and no 
warranties or representations are made or intended to persons or entities not 
named above.  If the reader is not the intended recipient, you are hereby 
notified that any dissemination, distribution or copying of this communication 
is strictly prohibited.  If you have received this communication in error, 
please notify us immediately by telephone, return this message to the address 
above and delete all copies.  Thank you.

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to