Dave, '10 Handbook, 10.10.2.2, "The trench must be backfilled prior to hydrostatic testing to prevent movement of underground piping. The backfilling can take place between joints if it is desired to observe the joints for leakage and if the backfill depth is sufficient to prevent movement..."
Scott Futrell (763) 425-1001 Office (612) 759-5556 Cell -----Original Message----- From: [email protected] [mailto:[email protected]] On Behalf Of David de Vries Sent: Tuesday, August 03, 2010 12:24 PM To: AFSA SprinklerForum Subject: Leaking Lead-In I am looking at a new lead-in that was hydro-tested after being backfilled and the floor slab poured over it. It failed the hydrotest. I went to look up in 13 and 24 the "requirement" that underground piping be tested before being buried. I can't find it. Is my memory bad (no comments about old age, Ron, please) or am I perhaps thinking of a best practice that I previously included in a spec? Any help in finding that would be appreciated. Dave David A. de Vries, P.E., CSP Firetech Engineering Incorporated _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [email protected] To Unsubscribe, send an email to:[email protected] (Put the word unsubscribe in the subject field) _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [email protected] To Unsubscribe, send an email to:[email protected] (Put the word unsubscribe in the subject field)