Sounds like your consultant is correct in accordance with NFPA 13.  But that
does not address whether there are any specially adopted requirements via
the Department  of Health.

Jeff Hewitt, PE, SET, SFPE (Professional Member)
Corporate Engineer
Bi-State Fire Protection Corporation

241 Hughes Lane
St. Charles, MO  63301
636-946-0011
636-946-5172 (fax)
314-574-6989 (cell)

Fire Sprinklers Save lives.
Can You Live Without Them?

-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Dennis
Schwarzauer
Sent: Friday, August 20, 2010 3:47 PM
To: [email protected]
Subject: Question on sprinklering an attic space

I have a single story residential-style structure used for housing
semi-dependent residents for the State Department of Mental Health. The unit
is an Intermediate Care Facility for the Mentally Retarded, but is viewed as
a nursing home by the state agencies.

The building is non-combustible construction; CMU bearing walls with light
gauge metal trusses and standing seam metal roof. The single floor is fully
sprinklered & that is where my problem begins. My boss had me direct the
Consultants to eliminate the sprinkler in the attic, to save money, as the
building was of non-combustible construction. Now the Fire Marshal &
reviewer for the State Health Department are telling me that  all the PVC
vent stacks and piping insulation is non-compliant.

My Consultant is telling me that, as these are concealed spaces, the IBC
allows non-combustible & limited combustible materials to be present without
sprinklers.

Any thoughts?

Thanks,

Dennis M. Schwarzauer

Eley Guild Hardy Architects PA
418 East Capitol Street
Jackson, Mississippi  39201
T 601.354.2572
F 601.355.2006
www.eleyguildhardy.com
P Please consider the environment before printing this e-mail

This email and any files transmitted with it are confidential and intended
solely for the use of the individual or entity to whom they are addressed.
If you have received this email in error please notify us immediately by
replying to the sender and deleting this copy from your system. Please note
that any views or opinions presented in this email are solely those of the
author and do not necessarily represent those of Eley Guild Hardy Architects
PA.  Finally, the recipient should check this email and any attachments for
the presence of viruses. Eley Guild Hardy Architects PA accepts no liability
for any damage caused by any virus transmitted by this email.

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to