2006 IBC 717.5 Combustible materials in concealed spaces in Type I or II construction. Combustible materials shall not be permitted in concealed spaces of buildings of Type I or II construction.
Exceptions: 1. Combustible materials in accordance with Section 603. 2. Combustible materials exposed within plenums complying with Section 602 of the International Mechanical Code. 3. Class A interior finish materials classified in accordance with Section 803. 4. Combustible piping within partitions or shaft enclosures installed in accordance with the provisions of this code. 5. Combustible piping within concealed ceiling spaces installed in accordance with the International Mechanical Code and the International Plumbing Code. 6. Combustible insulation and covering on pipe and tubing, installed in concealed spaces other than plenums, complying with Section 719.7. John Drucker, CET Fire Protection Subcode Official Fire/Building/Electrical Inspector Fire Marshals Office Borough of Red Bank, NJ -----Original Message----- From: [email protected] [mailto:[email protected]] On Behalf Of [email protected] Sent: Saturday, August 21, 2010 10:21 AM To: A.P.Silva; [email protected] Subject: Re: Question on sprinklering an attic space S Sent from my Verizon Wireless Phone ----- Reply message ----- From: "A.P.Silva" <[email protected]> Date: Fri, Aug 20, 2010 5:40 pm Subject: Question on sprinklering an attic space To: <[email protected]> I think the point is you have combustible construction (pvc vent stacks & combustible pipe insulation) in a building designated as non-combustible. The question is not only whether you need sprinklers in this concealed space but also whether you can have combustible material in a non-combustible building. You will have to look at your building code. Certain combustible material such as millwork and combustible sprinkler piping may be permitted, but most other combustible material may not be. Providing sprinklers in this concealed space may not be a solution, although it may be used to obtain a variance. I really don't understand the advice given by your consultant and what bearing it has on this issue. Are they saying all material in the concealed space are either non-combustible or limited combustible? You need to find out if this is correct. I think you are confusing two issues here. This is not primarily a sprinkler issue, but whether you are are allowed certain combustible material in a non-combustible building. Tony -----Original Message----- From: [email protected] [mailto:[email protected]] On Behalf Of Jeff Hewitt Sent: August 20, 2010 3:13 PM To: [email protected] Subject: RE: Question on sprinklering an attic space Sounds like your consultant is correct in accordance with NFPA 13. But that does not address whether there are any specially adopted requirements via the Department of Health. Jeff Hewitt, PE, SET, SFPE (Professional Member) Corporate Engineer Bi-State Fire Protection Corporation 241 Hughes Lane St. Charles, MO 63301 636-946-0011 636-946-5172 (fax) 314-574-6989 (cell) Fire Sprinklers Save lives. Can You Live Without Them? -----Original Message----- From: [email protected] [mailto:[email protected]] On Behalf Of Dennis Schwarzauer Sent: Friday, August 20, 2010 3:47 PM To: [email protected] Subject: Question on sprinklering an attic space I have a single story residential-style structure used for housing semi-dependent residents for the State Department of Mental Health. The unit is an Intermediate Care Facility for the Mentally Retarded, but is viewed as a nursing home by the state agencies. The building is non-combustible construction; CMU bearing walls with light gauge metal trusses and standing seam metal roof. The single floor is fully sprinklered & that is where my problem begins. My boss had me direct the Consultants to eliminate the sprinkler in the attic, to save money, as the building was of non-combustible construction. Now the Fire Marshal & reviewer for the State Health Department are telling me that all the PVC vent stacks and piping insulation is non-compliant. My Consultant is telling me that, as these are concealed spaces, the IBC allows non-combustible & limited combustible materials to be present without sprinklers. _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [email protected] To Unsubscribe, send an email to:[email protected] (Put the word unsubscribe in the subject field) _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [email protected] To Unsubscribe, send an email to:[email protected] (Put the word unsubscribe in the subject field)