No, in a typical NFPA 25 inspection the inspector should not document a room missing sprinklers if the room and sprinkler layout was approved by the AHJ. That is why the owner of the system should be asked if there were any changes made to the system or building since the last inspection. If changes were made, the owner should be advised to have a system evaluation performed to determine if the system needs modified to accomodate changes.
Forest Wilson
Cherokee Fire

On 8/30/2010 11:24 AM, Greg McGahan wrote:

What about when doing inspections per 25? If you had a room with no heads in it inside the building aren't you supposed to write it up? And I agree with you about the EOR thing except ( EVERYONE PLEASE DO NOT START A WHOLE THREAD ABOUT THIS AGAIN) when we have the note that says "protect per NFPA #13"..... I would really like a definitive answer.

Having a Great Day,
Greg
On 8/30/2010 8:34 AM, George Church wrote:
Greg, it sounds like you're defining the scope of your work like an Engineer
of Record would do.

The TC list is on the nfpa codes and stds website, and both AFSA and NFSA will provide "informal interpretations for members- we use this frequently to provide documentation to support our position when the AHJ interp differs
from what we read.

I had a fire official who didn't believe a pump could supply more than one
building. Now any big industrial complex with a pump and tank- or more-
usually feeds more than one building, but he wanted some proof. I requested a letter (actually a REPLY) from a couple committee members of both 13 and 20, the applicable standards, and he accepted them as sufficient evidence what we proposed met the intent of the committee. So there's another reason to go to AFSA's convention, it s more likely you'll get a letter back from a TC member if you've bought em a refreshment or at least bothered to show up at convention and met em. Otherwise you're liable to be classified as one who asks questions he could look up, and lazy isn't a reason for bothering
the TC members.

Those pump letters spared my customer something like a dozen pumps, some
13Ds, some 20's. Any question that membership in our associations and
attendance at convention allows you the tools to properly serve your
customers? I saw a competitor's proposal on Friday that stated their
insurance company does not allow them to do anything that isn't in the code. By inference, I'm thinking performance-based design and anything under 1.4 Equivalency isn't touched with a 10-foot pole. I like that because there
are times when alternative means and methods make sense and a strict
adherence to the applicable standard doesn't, not to mention a couple
million dollars in Quell jobs we've done. Be sure to provide written
substantiation to the AHJ supporting your Equivalency, produced by someone
competent to write the documentation, or you're just outside the code.

glc

-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Greg McGahan
Sent: Monday, August 30, 2010 9:12 AM
To: [email protected]
Subject: Re: 2010 handling and storage of combustibles

Thanks for the debate but is there anyone on the committee that can help?

What about the most common overhang we see in these situations: hangs over the truck to keep things dry while entering the building, there is no "dock"
under the Overhang.

When we try to protect it and also get paid for doing so, what do I hang my liability hat on with the legalists out there? "It doesn't say handled, and
sitting out there for a few hours is not stored" Can't you hear it now?

On 8/30/2010 8:07 AM, [email protected] wrote:
It's just the nature of the beast.  There are a lot of things not
clarified or defined in the Codes.
My biggest challenge right now being the occupancy classification of a
machine shop, architects have one idea, engineers and operators another.
Only those who put these undefined categories in the Codes know what is what
for sure.
Anyway, back to our regularly scheduled topic.....................

Craig L. Prahl, CET
Fire Protection Specialist
Mechanical Department
CH2MHILL
Lockwood Greene
1500 International Drive
Spartanburg, SC  29304-0491
Direct - 864.599.4102
Fax - 864.599.8439
[email protected]
http://www.ch2m.com


-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Todd
Williams
Sent: Monday, August 30, 2010 8:54 AM
To: [email protected]
Subject: RE: 2010 handling and storage of combustibles

Then why doesn't NFPA and/or the Building Codes state that? (i.e not
include it in the same section as porte cochere). It would make our
lives easier.

A8.15.7.5 describes "Short-term transient storage"  and states that it
should not be considered storage or handing of combustibles. So if a
pallet of goods is put down on a dock while a truck is being loaded
and organized for deliveries, would that be short-term transient
storage? I think the original question was in effect, what constitutes
"short-term"? Legit question. Goes back to my unattended comment.

I know appendix material is not part of the standard, however, it is
quite frequently either incorporated into Code or used for interpretation.



At 08:49 AM 8/30/2010, you wrote:
Exactly. That's why you protect it if its intended use is storage.
We're not the police.

A congregation just moved into their new church we sprinklered after
29 years in their "temporary" sanctuary. Nuff said?

glc

-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Todd
Williams
Sent: Monday, August 30, 2010 8:37 AM
To: [email protected]
Subject: RE: 2010 handling and storage of combustibles

If a pallet touches the ground, it's storage? Difficult to police in
real life.



At 08:26 AM 8/30/2010, you wrote:
"..not ever stored.." means they are NEVER placed there for any
reason ever.   I have had the pleasure of playing semantics with
those who will say, "they are STAGED, not stored", when I ask for
how long, well that depends, might be a few hours, might be a few
days.  So
>from a personal standpoint, staging, handling, storage are
all treated as storage.   If there is any chance that any
combustible commodities will be placed within the area for any
length of time, it's a potential STORAGE area.

Craig L. Prahl, CET
Fire Protection Specialist
Mechanical Department
CH2MHILL
Lockwood Greene
1500 International Drive
Spartanburg, SC  29304-0491
Direct - 864.599.4102
Fax - 864.599.8439
[email protected]
http://www.ch2m.com

-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Greg
McGahan
Sent: Saturday, August 28, 2010 10:46 PM
To: [email protected]
Subject: 2010 handling and storage of combustibles

    Can someone please look in the 2010 handbook and tell me what the
intent of 8.15.7.1, 2 and 5 is? According to the way I read it -

.1 states that all overhangs over 4' wide need protection UNLESS
.2,.3 or .4 are met.
.2 states that protection can be omitted if the overhang is over 4'
wide and made of Non-comb material
.5 states that protection is required if the overhang is OVER 2'
wide and combustible materials are STORED

Therefore, if you have a noncombustible canopy that is over 4'-0"
wide where combustibles are loaded and unloaded but not stored then
protection is not required regardless of the size of the overhang?

So now we could have a canopy that covers thousands of square feet
and yet materials are not ever "stored" under them and protection is
not required?


_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to:
[email protected]

To Unsubscribe, send an email
to:[email protected]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to:
[email protected]

To Unsubscribe, send an email
to:[email protected]
(Put the word unsubscribe in the subject field)
Todd G. Williams, PE
Fire Protection Design/Consulting
Stonington, CT
860.535.2080
www.fpdc.com

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email
to:[email protected]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email
to:[email protected]
(Put the word unsubscribe in the subject field)
Todd G. Williams, PE
Fire Protection Design/Consulting
Stonington, CT
860.535.2080
www.fpdc.com

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email
to:[email protected]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email
to:[email protected]
(Put the word unsubscribe in the subject field)
--
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)


_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to