I would lean toward exposed pipe dope. It separates and must be stirred
occasionally. The oily substance I have found on sprinklers looks just like
the oil in the compound. If it were from the fittings, I would almost
certainly think we would see water. Since most helpers (I in the day) use
the glob/brush method, I would think there is enough outside the threads to
separate over time. Even years.

R/
Matt

  

Matthew J. Willis, CET
Automatic Fire Sprinklers
Norred Fire Systems L.L.C.
318-387-1134 Voice
318-816-1087 Mobile
318-387-1163 Facsimile
[email protected]

> >-----Original Message-----
> >From: [email protected] [mailto:sprinklerforum-
> >[email protected]] On Behalf Of Matt Grise
> >Sent: Friday, September 10, 2010 4:14 PM
> >To: '[email protected]'
> >Subject: RE: oily substance on sprinkler deflectors
> >
> >What environment are the heads in? what is the space used for?
> >
> >Matt Grisé PE*, LEED AP
> >Sales Engineer
> >Alliance Fire Protection
> >*Licensed in KS & MO
> >
> >913.888.0647 ph
> >913.888.0618 f
> >913.927.0222 cell
> >www. AFPsprink.com
> >
> >
> >-----Original Message-----
> >From: [email protected] [mailto:sprinklerforum-
> >[email protected]] On Behalf Of Forest Wilson
> >Sent: Friday, September 10, 2010 4:12 PM
> >To: [email protected]
> >Subject: oily substance on sprinkler deflectors
> >
> >  Question: I surveyed a sprinkler system today, installed 2001.
> >Wet System; Steel Pipe; SSP heads
> >About half the deflectors have a oily substance on them. The occupant
> >wiped the deflectors clean 2 years ago, but they are oily again.
> >I assume this is pipe joint compound or cutting oil leaking through the
> >fittings.
> >Am I correct in this assumption?
> >What causes this?
> >
> >Forest Wilson
> >Cherokee Fire
> >
> >
> >On 9/10/2010 3:42 PM, Ed Kramer wrote:
> >> I've heard that the intent of 903.3.1.2.1 is to protect the structure
> >from
> >> fires that start on the patio/deck/balcony, and in particular from
> >fires
> >> that are started by cooking equipment (BBQ/grills).  Assuming that's
> >the
> >> case, your balcony shouldn't be required to be protected.  I'll be up
> >to you
> >> to get the AHJ's blessing to delete the sprinkler protection, but I
> >think
> >> you'd have a very good argument.
> >>
> >> Ed Kramer
> >> Littleton, CO
> >>
> >>> I have a question about an R2 occupancy I'm working on.  This relates
> >to
> >>> 903.3.1.2.1 in the 2009 IBC.  This living facility has what I would
> >>> consider
> >>> fake patios on some of the rooms.  They are shallow, only about 3'
> >wide,
> >>> and
> >>> they are not normally useable.  What I mean by that is there are
> >>> railings at
> >>> the outside edge with no openings, and there are no doors accessing
> >them
> >>> from the dwelling unit.  So to get onto this thing, you would have to
> >>> hop
> >>> the railing or crawl through a normal size window.  I couldn't find a
> >>> definition in the IBC for whether a patio/deck /balcony is only
> >>> considered
> >>> that if its accessible or not.
> >>>
> >>> This building is definitely type V construction, so this would apply,
> >>> but
> >>> does the IBC make any differentiation in terms of the balcony being
> >>> accessible, or just being an architectural feature.  Has anyone
> >>> encountered
> >>> this before?
> >>>
> >>> The other slight issue is that technically the code being enforced
> >still
> >>> references the 2006 IBC, but I only have a 2009 copy.  I can't hope
> >that
> >>> this was new, can I?
> >>>
> >>> I actually have a rendered image of what I'm talking about if that
> >>> helps.
> >>> http://www.bseg-ce.com/port_hopewell.html
> >>> Look at the two first floor cut-ins on either side of the person in
> >that
> >>> rendering to see what I'm talking about.
> >>>
> >>> Any help would be appreciated.
> >>>
> >>> Thanks,
> >>>
> >>> Benjamin Young, CET
> >>> Sobieski Fire Protection
> >> _______________________________________________
> >> Sprinklerforum mailing list
> >> [email protected]
> >> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
> >>
> >> For Technical Assistance, send an email to: [email protected]
> >>
> >> To Unsubscribe, send an email to:Sprinklerforum-
> >[email protected]
> >> (Put the word unsubscribe in the subject field)
> >
> >_______________________________________________
> >Sprinklerforum mailing list
> >[email protected]
> >http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
> >
> >For Technical Assistance, send an email to: [email protected]
> >
> >To Unsubscribe, send an email to:[email protected]
> >(Put the word unsubscribe in the subject field)
> >_______________________________________________
> >Sprinklerforum mailing list
> >[email protected]
> >http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
> >
> >For Technical Assistance, send an email to: [email protected]
> >
> >To Unsubscribe, send an email to:[email protected]
> >(Put the word unsubscribe in the subject field)
> >
> >No virus found in this incoming message.
> >Checked by AVG - www.avg.com
> >Version: 9.0.851 / Virus Database: 271.1.1/3124 - Release Date: 09/10/10
> >02:08:00

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to