And if you just have Q, convert to ft^3/sec, convert 1.75" diam to ft^2,
divide 1st by 2nd to get ft/sec, h=v^2/2g, P= h x .433. (coefficient of
discharge for monitor noz might be about .98, g=32.2 ft/sec^2)

-----Original Message-----
From: Richard Carr [mailto:[email protected]] 
Sent: Thursday, September 16, 2010 8:39 AM
To: [email protected]
Subject: RE: Monitor nozzle 

K= Q DIVIDED BY SQUARE ROOT OF P, So if you have your Q and P you can
get your K.

Richard Carr, SET
Design Manager
Associated Sprinkler Co., LLC
336.373.3901 ext 217
[email protected]




-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of
Jamie.seidl
Sent: Thursday, September 16, 2010 9:33 AM
To: Afsa
Subject: Monitor nozzle 

Does anyone have a k factor equivalent for a 1-3/4" monitor nozzle?

Jamie
Sent from my iPhone
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email
to:[email protected]
(Put the word unsubscribe in the subject field)


This email and any attached files are confidential and intended solely for
the intended recipient(s). If you are not the named recipient you should not
read, distribute, copy or alter this email. Any views or opinions expressed
in this email are those of the author and do not represent those of the
company. Warning: Although precautions have been taken to make sure no
viruses are present in this email, the company cannot accept responsibility
for any loss or damage that arise from the use of this email or attachments.
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to