Sorry guys, correction

The requirement applies to all.  

5.12 is Equipment Protection

5.12.1.2, 5.12.1.2.1 & 5.12.1.2.2 is Outdoor Fire Pump Units

5.12.5 is its own section.

5.12.5 Ventilation. Provision shall be made for ventilation of a pump room
or pump house.

Yes even AHJ's need to take a second look. Provide ventilation.

John



-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of John Drucker
Sent: Thursday, September 16, 2010 11:48 AM
To: [email protected]
Subject: RE: Pump Rooms

Yes, However the cited standards reference applies to Outdoor Fire Pump
Units.

5.12.1.2 Outdoor Fire Pump Units.

John Drucker, CET
Fire Protection Subcode Official 
Fire/Building/Electrical Inspector
Fire Marshals Office
Borough of Red Bank, NJ



-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Brian Harris
Sent: Thursday, September 16, 2010 11:27 AM
To: [email protected]
Subject: Pump Rooms

What's the consensus on ventilating pump rooms? 5.12.5 (NFPA 20) Says that
provisions for ventilation need to be made, is this for all pump rooms or
diesel only? I'm getting conflicting stories from the AHJ & the pump rep.

 

Brian Harris

First Defense Fire Protection

11957 Ramah Church Road

Huntersville, NC 28078

Phone: 704.948.3506

Fax: 704.948.3507

Nicet # 128476

 





=======
Email scanned by PC Tools - No viruses or spyware found.
(Email Guard: 7.0.0.21, Virus/Spyware Database: 6.15890)
http://www.pctools.com/
=======
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to