The ventilation requirements for Diesel pump installations is definitely a
lot more in depth.  See 11.3 in the 2010 edition.  Its not just for the
combustion air, its also for cooling.

Benjamin Young



On Thu, Sep 16, 2010 at 11:55 AM, John Drucker <[email protected]>wrote:

> Sorry guys, correction
>
> The requirement applies to all.
>
> 5.12 is Equipment Protection
>
> 5.12.1.2, 5.12.1.2.1 & 5.12.1.2.2 is Outdoor Fire Pump Units
>
> 5.12.5 is its own section.
>
> 5.12.5 Ventilation. Provision shall be made for ventilation of a pump room
> or pump house.
>
> Yes even AHJ's need to take a second look. Provide ventilation.
>
> John
>
>
>
> -----Original Message-----
> From: [email protected]
> [mailto:[email protected]] On Behalf Of John
> Drucker
> Sent: Thursday, September 16, 2010 11:48 AM
> To: [email protected]
> Subject: RE: Pump Rooms
>
> Yes, However the cited standards reference applies to Outdoor Fire Pump
> Units.
>
> 5.12.1.2 Outdoor Fire Pump Units.
>
> John Drucker, CET
> Fire Protection Subcode Official
> Fire/Building/Electrical Inspector
> Fire Marshals Office
> Borough of Red Bank, NJ
>
>
>
> -----Original Message-----
> From: [email protected]
> [mailto:[email protected]] On Behalf Of Brian
> Harris
> Sent: Thursday, September 16, 2010 11:27 AM
> To: [email protected]
> Subject: Pump Rooms
>
> What's the consensus on ventilating pump rooms? 5.12.5 (NFPA 20) Says that
> provisions for ventilation need to be made, is this for all pump rooms or
> diesel only? I'm getting conflicting stories from the AHJ & the pump rep.
>
>
>
> Brian Harris
>
> First Defense Fire Protection
>
> 11957 Ramah Church Road
>
> Huntersville, NC 28078
>
> Phone: 704.948.3506
>
> Fax: 704.948.3507
>
> Nicet # 128476
>
>
>
>
>
>
>
> =======
> Email scanned by PC Tools - No viruses or spyware found.
> (Email Guard: 7.0.0.21, Virus/Spyware Database: 6.15890)
> http://www.pctools.com/
> =======
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> For Technical Assistance, send an email to: [email protected]
>
> To Unsubscribe, send an email 
> to:[email protected]<to%[email protected]>
> (Put the word unsubscribe in the subject field)
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> For Technical Assistance, send an email to: [email protected]
>
> To Unsubscribe, send an email 
> to:[email protected]<to%[email protected]>
> (Put the word unsubscribe in the subject field)
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> For Technical Assistance, send an email to: [email protected]
>
> To Unsubscribe, send an email 
> to:[email protected]<to%[email protected]>
> (Put the word unsubscribe in the subject field)
>
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to