And what is the C factor of any given system but a guess? I just saw a
picture of a relatively new system (five years) that had complete
clogging of some pipes. C = 0? I'm surprised your AHJ didn't make you
calculate for each pipe one diameter smaller than the installed size
so as to adjust for age shrinkage.

On Thu, Sep 16, 2010 at 9:23 AM, Thom <[email protected]> wrote:
>
> Then there's always the question of what C factor to use in your calc's of
> an old PS system? Have you seen the inside of these pipes? Do you use 120 or
> 100 or maybe even 80? There is really no guide on what's appropriate. I had
> one AHJ that just wanted the calc to fail, and required that we use a C of
> 80, when that calc still worked, he said oh I meant 60.
> There was a fight but we ended up doing an internal inspection of the pipe
> and he accepted the calc that used 80. (Still just a guess on his part.)
>
> Thom
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> For Technical Assistance, send an email to: [email protected]
>
> To Unsubscribe, send an email to:[email protected]
> (Put the word unsubscribe in the subject field)
>



-- 
Ron Greenman
Instructor
Fire Protection Engineering Technology
Bates Technical College
1101 So. Yakima Ave.
Tacoma, WA 98405

[email protected]

http://www.bates.ctc.edu/fireprotection/

253.680.7346
253.576.9700 (cell)

Member:
AFSA, SFPE, ASCET, NFPA, NFSA, AFAA, ASEE, NIBS, WSAFM, WFC

They are happy men whose natures sort with their vocations. -Francis
Bacon, essayist, philosopher, and statesman (1561-1626)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to