C value for new steel 140, we use 120 Wet, 100 Dry to allow for age. There
are systems out there approaching 30 years that were calculated (+/-). I
wonder the condition of these. Was the 120/100 used correct? I would think
not based on the inside of piping I have seen over the years. The flushing
required by 25 is a good starting point to control this. At what point
though do we consider the C worse that the allotted for aging?

R/
Matt 

 

Matthew J. Willis, CET
Automatic Fire Sprinklers
Norred Fire Systems L.L.C.
318-387-1134 Voice
318-816-1087 Mobile
318-387-1163 Facsimile
[email protected]

> >-----Original Message-----
> >From: [email protected] [mailto:sprinklerforum-
> >[email protected]] On Behalf Of Ron Greenman
> >Sent: Thursday, September 16, 2010 11:30 AM
> >To: [email protected]
> >Subject: Re: Pipe Schedule Systems
> >
> >And what is the C factor of any given system but a guess? I just saw a
> >picture of a relatively new system (five years) that had complete
> >clogging of some pipes. C = 0? I'm surprised your AHJ didn't make you
> >calculate for each pipe one diameter smaller than the installed size
> >so as to adjust for age shrinkage.
> >
> >On Thu, Sep 16, 2010 at 9:23 AM, Thom <[email protected]> wrote:
> >>
> >> Then there's always the question of what C factor to use in your calc's
> >of
> >> an old PS system? Have you seen the inside of these pipes? Do you use
> >120 or
> >> 100 or maybe even 80? There is really no guide on what's appropriate. I
> >had
> >> one AHJ that just wanted the calc to fail, and required that we use a C
> >of
> >> 80, when that calc still worked, he said oh I meant 60.
> >> There was a fight but we ended up doing an internal inspection of the
> >pipe
> >> and he accepted the calc that used 80. (Still just a guess on his
> >part.)
> >>
> >> Thom
> >>
> >> _______________________________________________
> >> Sprinklerforum mailing list
> >> [email protected]
> >> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
> >>
> >> For Technical Assistance, send an email to: [email protected]
> >>
> >> To Unsubscribe, send an email to:Sprinklerforum-
> >[email protected]
> >> (Put the word unsubscribe in the subject field)
> >>
> >
> >
> >
> >--
> >Ron Greenman
> >Instructor
> >Fire Protection Engineering Technology
> >Bates Technical College
> >1101 So. Yakima Ave.
> >Tacoma, WA 98405
> >
> >[email protected]
> >
> >http://www.bates.ctc.edu/fireprotection/
> >
> >253.680.7346
> >253.576.9700 (cell)
> >
> >Member:
> >AFSA, SFPE, ASCET, NFPA, NFSA, AFAA, ASEE, NIBS, WSAFM, WFC
> >
> >They are happy men whose natures sort with their vocations. -Francis
> >Bacon, essayist, philosopher, and statesman (1561-1626)
> >_______________________________________________
> >Sprinklerforum mailing list
> >[email protected]
> >http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
> >
> >For Technical Assistance, send an email to: [email protected]
> >
> >To Unsubscribe, send an email to:[email protected]
> >(Put the word unsubscribe in the subject field)
> >No virus found in this incoming message.
> >Checked by AVG - www.avg.com
> >Version: 9.0.851 / Virus Database: 271.1.1/3137 - Release Date: 09/16/10
> >01:34:00

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to